johanza24 Posted December 12, 2020 Share Posted December 12, 2020 Do you have any knowledge of earth leakage not tripping when tested with meter from plug, when on inverter power? I have change-over switch between Eskom and inverter power feeding the earth leakage to all circuits in house. Any advice/feedback Johan Quote Link to comment Share on other sites More sharing options...
Richard Mackay Posted December 12, 2020 Share Posted December 12, 2020 How are you testing the EL? Quote Link to comment Share on other sites More sharing options...
johanza24 Posted December 13, 2020 Author Share Posted December 13, 2020 Hi V, It trips when you press test button. First time delayed response. Thereafter trips when you press. Quote Link to comment Share on other sites More sharing options...
johanza24 Posted December 13, 2020 Author Share Posted December 13, 2020 It did not trip on the in-plug tester at 35-40ma setting. Quote Link to comment Share on other sites More sharing options...
Richard Mackay Posted December 13, 2020 Share Posted December 13, 2020 23 hours ago, johanza24 said: Do you have any knowledge of earth leakage not tripping when tested with meter from plug, when on inverter power? Does it trip ok when on mains power? Quote Link to comment Share on other sites More sharing options...
DDD Posted December 13, 2020 Share Posted December 13, 2020 Is the neutral of the inverter also ("properly") earthed? Quote Link to comment Share on other sites More sharing options...
johanza24 Posted December 13, 2020 Author Share Posted December 13, 2020 Hi Rich It did trip on grid mains, however at higher than the 30ma., Between 35-40ma. Just tested by pressing test button, works fine on inverter power. I am suspecting the earth leakage device [RCD]. Obtained a new device will get electrician to fit and test again. Thanks. Quote Link to comment Share on other sites More sharing options...
johanza24 Posted December 13, 2020 Author Share Posted December 13, 2020 Hi Erastus, According to the wiring diagram of the installation manual for 5kW Deye the only earth required was between the inverter body and DB earth, which is done. As said I will retest everything after replacing the earth leakage device [RCD] The inverter neutral properly earthed?? What are you meaning by this? Thanks. Quote Link to comment Share on other sites More sharing options...
Gerrie Posted December 13, 2020 Share Posted December 13, 2020 5 hours ago, johanza24 said: e inverter neutral properly earthed?? What are you meaning by this? Some inverters like my own Axpert clone need the bonding between neutral and earth before it would trip with the E/L tester, without the bonding it will not trip the earth leakage. Richard Mackay 1 Quote Link to comment Share on other sites More sharing options...
johanza24 Posted December 15, 2020 Author Share Posted December 15, 2020 Thanks everyone for your feedback and advice. We replaced the earth leak switch and problem solved. Exchanged the Lesco with a Fleischer. Viola!! Quote Link to comment Share on other sites More sharing options...
Choto Posted February 23, 2023 Share Posted February 23, 2023 @johanza24 when you say you changed the earth leak switch, do you mean you changed the earth leakage breaker in the DB board? Quote Link to comment Share on other sites More sharing options...