December 12, 20205 yr Do you have any knowledge of earth leakage not tripping when tested with meter from plug, when on inverter power? I have change-over switch between Eskom and inverter power feeding the earth leakage to all circuits in house. Any advice/feedback Johan
December 13, 20205 yr Author Hi V, It trips when you press test button. First time delayed response. Thereafter trips when you press.
December 13, 20205 yr 23 hours ago, johanza24 said: Do you have any knowledge of earth leakage not tripping when tested with meter from plug, when on inverter power? Does it trip ok when on mains power?
December 13, 20205 yr Author Hi Rich It did trip on grid mains, however at higher than the 30ma., Between 35-40ma. Just tested by pressing test button, works fine on inverter power. I am suspecting the earth leakage device [RCD]. Obtained a new device will get electrician to fit and test again. Thanks.
December 13, 20205 yr Author Hi Erastus, According to the wiring diagram of the installation manual for 5kW Deye the only earth required was between the inverter body and DB earth, which is done. As said I will retest everything after replacing the earth leakage device [RCD] The inverter neutral properly earthed?? What are you meaning by this? Thanks.
December 13, 20205 yr 5 hours ago, johanza24 said: e inverter neutral properly earthed?? What are you meaning by this? Some inverters like my own Axpert clone need the bonding between neutral and earth before it would trip with the E/L tester, without the bonding it will not trip the earth leakage.
December 15, 20205 yr Author Thanks everyone for your feedback and advice. We replaced the earth leak switch and problem solved. Exchanged the Lesco with a Fleischer. Viola!!
February 23, 20233 yr @johanza24 when you say you changed the earth leak switch, do you mean you changed the earth leakage breaker in the DB board?