Earth leakage not tripping


johanza24

Recommended Posts

Hi Rich

It did trip on grid mains, however at higher than the 30ma.,  Between 35-40ma.

Just tested by pressing test button, works fine on inverter power.

I am suspecting the earth leakage device [RCD].  Obtained a new device will get electrician to fit and test again.

Thanks.

Link to comment
Share on other sites

Hi Erastus,

According to the wiring diagram of the installation manual for 5kW Deye the only earth required was between the inverter body and DB earth, which is done.

As said I will retest everything after replacing the earth leakage device [RCD]

 

The inverter neutral properly earthed??  What are you meaning by this?

Thanks.