December 25, 20205 yr Morning gents. I have a deye 5kw pure sine wave hybrid. I noticed when there is no battery connected the Grid tie fuction works correct. When I ad my Pylontech battery, all extra capacity feeds into the Grid. Any idea as the CT clamps is installed as per the schetch, I have turned it around as well.
December 25, 20205 yr Can you share your screens. I have the sunsynk but the only difference would be the user interface. You need to select "zero export to CT"
December 25, 20205 yr Author I have tried that. It atill export, it is as if the CT gets ignored. I have turned it around, diconnected from the live. When the inverter has no battery connected/disabled then it works fine no feedback. As sson as I enable the Litium settings and the inverter restarts with the setiingd on Zero export to CT it still exports to the Grid. Will send some photos in a few.
December 25, 20205 yr Can't seem to open any of the files in my phone. The best option I found to upload pics is to take the pic with the phone and do a screenshot of the pic. This will get the size if the photo shown so you can upload the screenshot instead of the full picture.