KobusK Posted December 25, 2020 Share Posted December 25, 2020 Morning gents. I have a deye 5kw pure sine wave hybrid. I noticed when there is no battery connected the Grid tie fuction works correct. When I ad my Pylontech battery, all extra capacity feeds into the Grid. Any idea as the CT clamps is installed as per the schetch, I have turned it around as well. Quote Link to comment Share on other sites More sharing options...
Achmat Posted December 25, 2020 Share Posted December 25, 2020 Can you share your screens. I have the sunsynk but the only difference would be the user interface. You need to select "zero export to CT" Quote Link to comment Share on other sites More sharing options...
KobusK Posted December 25, 2020 Author Share Posted December 25, 2020 I have tried that. It atill export, it is as if the CT gets ignored. I have turned it around, diconnected from the live. When the inverter has no battery connected/disabled then it works fine no feedback. As sson as I enable the Litium settings and the inverter restarts with the setiingd on Zero export to CT it still exports to the Grid. Will send some photos in a few. Quote Link to comment Share on other sites More sharing options...
KobusK Posted December 25, 2020 Author Share Posted December 25, 2020 Quote Link to comment Share on other sites More sharing options...
KobusK Posted December 25, 2020 Author Share Posted December 25, 2020 Quote Link to comment Share on other sites More sharing options...
Achmat Posted December 25, 2020 Share Posted December 25, 2020 Can't seem to open any of the files in my phone. The best option I found to upload pics is to take the pic with the phone and do a screenshot of the pic. This will get the size if the photo shown so you can upload the screenshot instead of the full picture. Quote Link to comment Share on other sites More sharing options...
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.