Earth leakage trips
Hi All
I am commissioning a Sunsynk 8KW with a Hubble AM2 while waiting for my PV's. At the monent I have a very expensive UPS.
When I cut the power to the inverter the switchover to battery is seamless. However when the power is switched on to the inverter the earth leakage trips after the anti islanding relay breaks contact. Any suggestions would be greatly appreciated. I have put my circuit diagram below.
11 minutes ago, TonyH said:
Hi, that will work but what protects anyone from working on the inverter?
You shouldn't be working on a live inverter.
The inverter should be fed by a double pole circuit breaker (fed directly from the mains) sized in accordance with the cable used and the inverter limits.
I had the same problem today ... I connected a 5 kva RCT inverter to a socket outlet (as a temp. supply to test and setup the unit before delivering to site) ... because the neutral and earth are bonded at the inverter output ... it will trip the mains earth leakage feeding the socket outlet ... so to setup the unit ... I removed the neutral earth bridge (which will be reconnected before the unit is delivered to site).
Edited by isetech