  1. Hello

     

    We would like to be able to see in real time the commands been send from an smart battery to an Axpert inverter. We have seen the inverter to react to the comments but we are not sure which commands the battery is sending.

    is there hardware which could be placed in the system to monitor the commands received by the inverter, we have the comm protocol table.

     

    Thanks

  2. Dear All,


    We have 2 x 5Kva Axperts, latest version, connected in parallel. These are set in SOL and with PV as the only charging method. For some reason once the PV array finalise charging the battery after a little while the inverters switch off the PV input (both of them) and start working from the battery (not from the grid) until the jump back to the grid voltage is reached at which point the battery will wait until next day to be recharged again.

    This is an inefficient usage of the inverter and once the battery is full we would like the PV to continue supplying the loads in parallel to the battery.

    If the PV isolator is reset the battery start charging inmediatelly while loads are as well supplied by the PV until is full at which point it again repeats the same cycle.

     

    Thanks for ideas on the settings.