Skip to content
View in the app

A better way to browse. Learn more.

Power Forum - Renewable Energy Discussion

A full-screen app on your home screen with push notifications, badges and more.

To install this app on iOS and iPadOS
  1. Tap the Share icon in Safari
  2. Scroll the menu and tap Add to Home Screen.
  3. Tap Add in the top-right corner.
To install this app on Android
  1. Tap the 3-dot menu (⋮) in the top-right corner of the browser.
  2. Tap Add to Home screen or Install app.
  3. Confirm by tapping Install.

Matteo_Mantovani

Members
  • Joined

  • Last visited

  1.    Matteo_Mantovani reacted to a post in a topic: Pylontech High Voltage Alarm
  2.    Matteo_Mantovani reacted to a post in a topic: Pylontech batteries Balancing
  3.    Matteo_Mantovani reacted to a post in a topic: Pylontech batteries Balancing
  4.    Matteo_Mantovani reacted to a post in a topic: Pylontech batteries Balancing
  5. sometimes I find in the early morning, after the night discharge, a situation with unbalanced batteries and some batteries well below 20%: Could it be a problem?
  6.    Matteo_Mantovani reacted to a post in a topic: Pylontech batteries Balancing
  7. For example today I have had: The max difference happen during the charge
  8. Since the last 3 batteries had the procedure from a technician to clear the EEPROM (to reset the fault). After the reset I saw that the SOC was changed immediately (about 10%) and the technician told me that the correspondence of voltage and SOC is back to normal
  9. no the battery have different age and also different fimware: Battery 1: FW V2.2 new chip ( age 1 month) Battery 2: FW V2.2 new chip ( age 1 month) Battery 3: FW V2.2 new chip ( age 1 month) Battery 4: FW V2.8 old chip ( age 2 years ) Battery 5: FW V2.8 old chip ( age 2 years ) Battery 6: FW V1.8 new chip ( age 5 month) The master have positive connected to the inverter + Tha last battery (n°6) have negative connected to the inverter - I try also to maintain the batteries connected toghether but not connected to the inverter for 6 hours to have a idle situation. When batteries reach the idle status I check the SOC but was different. Also I've seem that that this SOC differece non remain every time the same but in same case the different is 1-2%, specially in the evening when no big load or solar are present.
  10.    Matteo_Mantovani reacted to a post in a topic: Pylontech batteries Balancing
  11.    Matteo_Mantovani reacted to a post in a topic: Pylontech batteries Balancing
  12. Hi, I have had many problem of Over Voltage and after replace new batteries I tried to monitor the situation. I see that during the charge/discharge cycles the SOC values of the batteries are never the same SOC values but there is often a difference of 7/10%: I would like to understand if it is normal for the batteries to have a different SOC value even if the cells voltage are identical? The system consists of 6 US2000C pylontech batteries. Does this behavior happen to you too? Is there a way via commands sent to the battery to have a soc value corresponding to the voltage value? Thank you in advance
  13. Hi, I use MultiSIB software but I'm only able to see the data from batteries. I don't see any inverter data. Can someone help me understand why? I'm connected to the console port of the master battery Thank you
  14. Hi, I have a new US2000C battery (with a new chip) and the firmware installed is v2.2. I knew the latest was v1.8 but probably Pylontech has released a new firmware. Since I want to align all my batteries, does anyone have more information and where I can download this firmware? Thanks

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.