Axpert Inverter blew
Thank you so much @Coulomb Went to the site again today. Its the 145V 80A model. Jinko 555w panels. 8 groups of 2 in series with 2 inverters (4 groups per inverter). Checked the pv Voltage and each string was below 100V. Setup has been running fine for months. Inverters are second hand and one has been repaired due to generator damage (think the mppt was also replaced). Not sure which one was repaired. Repair was done before installation. Can i rule arcing or component failure?
-
Axpert Inverter blew
- Axpert Inverter blew
Hi all, would anyone be able to tell me what could have caused this failure on an Axpert inverter? Thanks- Axpert Fan Fault Error 01 - Repair
Thank you very much for the contact @Calvin Thank you very much @Coulomb for your input as well. If they are faulty would the main board need to be replaced?- Axpert Fan Fault Error 01 - Repair
Hi All, hope you are well So we moved our initial single phase installation (the smaller batteries and old inverters) to a new location and gave it new panels. Main location was upgraded to 3 Phase (2x 12kw 3P Deye's - very happy) New location Setup: 2x Axpert MKS 5K inverters connected to 16x 555w panels (each inverter with 4x sets of 2 panel strings - yes i know it took a lot of copper) One of the Axpert MKS 5K inverters recently started to get very "lazy". At times when i checked the pv coming in on the "good" inverter it would pull around 3.5kw while the "bad" one would only idle at around 200w PV in. The bad one would change its mind and would join the good one to draw more at times when it felt like it. The result would be that the good one would work about twice as hard as the bad one when you compare the total PV kWh over time. See screenshots attached. SolarMD has tried to assist by removing and changing the AxpertAI software presets (that controls the sytem on their logger) to no avail. Good inverter: Bad inverter: Now the bad inverter has started to give a 01 Error Fault. As far as i can gather its a fan fault and that i need specific fans to replace them. From what ive read the inverters can be picky on the type of fans it accepts even if the connector type and wire count is the same. Can anyone direct me to where i can get fans that can work on these models? Would this fix the 01 Error/is this the cause? Both fans are still spinning (up and down with load as well) and seems fine if observed. Would this fan fault error explain the "lazyness" we experienced earlier? Thank you very much!- Cheap Single-Phase Motor Soft Starter Module
Any update on how the soft starter worked?- New Deye inverters coming
Interesting, heard Keith also mention these coming soon. Any idea when they will be availableavailbe?- Deye 12kw 3-Phase optimal PV Configuration
- Deye 12kw 3-Phase optimal PV Configuration
Also just received an answer directly from Deye in China: Hello! As you have only provided me with the battery parameters, I have calculated with extreme low temperatures of -25 degrees Celsius. So only 13 can be accessed. If the minimum temperature is 0 degrees Celsius, then you can access 14. The reason for this difference is that - as the temperature decreases - the voltage of the solar modules increases. To ensure that the equipment is not damaged at the calculated low temperatures, so fewer modules may be connected the lower the temperature. I believe that he may have also given a recommendation of 5 modules regarding the minimum number of connections. But I think that 6 would give a more optimal working situation for the sake of a more stable operation of the mppt. Best wishes- Deye 12kw 3-Phase optimal PV Configuration
Source one: Aim for 550V. The VoC needs to be less than 800. VmP = 550V In terms of current it will draw what it can. Just don't exceed the relevant Voltages. Yes, 14 is good. Math works out. Source 2: Good day. You should be able to have two strings of 14 panels. I would not recommend 15 or 16 per string as it is too close to the voltage limit and you will loose 900W at peak production. Kind Regards- Deye 12kw 3-Phase optimal PV Configuration
Thank you for all your replies I have received back feedback from 2x very reputable sources (one is the inverter supplier) that 14 panels on a string is optimal- Deye 12kw 3-Phase optimal PV Configuration
Ok so i found something else that is interesting: https://www.sunsynk.org/3-phase-hybrid-inverter The exact Sunsynk equivalent model states the mppt range as 140 - 800V and the voltage sweetspot seems to be 450V- Deye 12kw 3-Phase optimal PV Configuration
Thank you for your reply @GreenFields Looking at this thread: Deye 12kw 3-Phase inverter MPPT question it seems as though 9S might perform un-optimally?- Deye 12kw 3-Phase optimal PV Configuration
Thank you @Scorp007 for your reply. So you are suggesting 3x strings of 14 panels in series? That would mean 23310W and be 7710w above the 15600W max DC input rating, would it not?- Deye 12kw 3-Phase optimal PV Configuration
Hi all, So im ready to acquire 2x Deye 12kw 3-Phase inverters (SUN-12K-SG04LP3-EU), but i need some assistance with the PV array configuration please: Inverter specs: Max. DC Input Power (W): 15600 Rated PV Input Voltage (V): 550(160~800) Start-up Voltage (V): 160 MPPT Voltage Range (V): 200-650 Full Load DC Voltage Range (V): 350-650 PV Input Current (A): 26+13 Max. PV ISC (A): 34+17 No.of MPP Trackers: 2 No.of Strings per MPP Tracker: 2+1 Im currently lookig at Jinko 555W (JKM555M-72HL4) panels due to cost. STC Specs: Voc: 49.72V Vmp: 40.99V Isc: 14.12A Imp: 13.54A Temperature coefficients of Voc: -0.28%/°C NOCT: 45±2°C From this i can gather the following (following: https://unboundsolar.com/blog/string-sizing-guide ) : Min string size: 6 panels (if i take the NOCT Vmp of 38.59V) : 200/38.59 and round up. Max strings size taking min temp (0°C where i live) into consideration: 14 panels: 800/49.72=16: 16*40.99 = 655.84 - too high so knock one down to 15 panels temp adjust: 49.72*0.0028 = 0.139216*47 = 6.543152+49.72= 56.27V max Voc at 0°C. Thus 56.27*15=843.95 - too high so knock one more down to 14 panels. Now for my question and for where im getting confused. 14 panels would mean 7770w - Can one Mppt string handle this amount of power? Would it clip or could it get damaged? If i aim for 5200w per string - that would mean 9 panels - it would mean my Vmp would only be 368.91 - which in turn would be too low to be optimal due to being to far from 550v. Is that correct? What would be optimal? Thank you so much - Axpert Inverter blew