Everything posted by PetCeres
-
Goodwe ES5048 & 3 X Pylontech US2000
Good day Is this Inverter still available? Petrus
-
Neutral/Earth bonding relay Goodwe ES inverters
Missed @weasel thread,🤔 Wired before the ELD.
-
Neutral/Earth bonding relay Goodwe ES inverters
-
Neutral/Earth bonding relay Goodwe ES inverters
Yes I drilled a 1.5 m earth spike into the ground with a big hammer outside the house and ground the inverter to it. Later I tested a 2 pole 10 amp relay and put the same ground on one N/C contact and on the com side, the neutral of the backup side of inverter. The N/O contact is wired to the N bar after main CB. The coil of the relay is been wired to the grid L&N after main CB, so when grid fails, relay de-energized, backup N is linked to new earth,93v floating is gone. May this be safe enough? Comment please!!!
-
Neutral/Earth bonding relay Goodwe ES inverters
Does anybody out there resolved this nuisance ELU trips after grid power restores?It only trips the backup side. I do measure 93v between E and N. thanks
-
Goodwe 5048ES Protocol reverse engineering
Subscribe!!! Would like to add my Goodwe ES to local Assistant
-
How to connect Solar System for home setup
Hi. I am new to this forum and that is the same route I would like to follow.I will follow this thread with interest.