September 21, 20214 yr Hi my name is Kevin. I need advise on a installation with 2 X 5kva Sunsynk inverters I have installed one on each phase and have the CTs on each phase at the meter box. The CT reading at this stage with very little load are 0 and as soon as I turn on the PV isolator it goes into negative numbers. Is it possible running back through the neutrals . Also what does the CT ratio need to be set at. Please advise Kevin Levin
September 21, 20214 yr Do you have single phase or three phase??? Your description refers to two phases. AFAIK that's not an option.
September 21, 20214 yr 8 minutes ago, Kevin Levin said: Hi my name is Kevin. I need advise on a installation with 2 X 5kva Sunsynk inverters I have installed one on each phase and have the CTs on each phase at the meter box. The CT reading at this stage with very little load are 0 and as soon as I turn on the PV isolator it goes into negative numbers. Is it possible running back through the neutrals . Also what does the CT ratio need to be set at. Please advise Kevin Levin Could you perhaps attch a few pictures of your wiring, db board etc.... it is quite uncommon to see a house with a two phase install.
September 21, 20214 yr 9 hours ago, Kevin Levin said: as soon as I turn on the PV isolator it goes into negative numbers That sounds like the CT’s are installed the wrong way, In the manual there is mention of negative Watt readings if coils are wrong way. 10 hours ago, Kevin Levin said: Also what does the CT ratio need to be set at. My 5KW ct ratio did not need to be set, it worked first time without setting.