October 20, 20214 yr Hey Guys.... I need help. 10X330Wp 5kw Sunsynk(CT coil) 2x3.5kw Pylontech Lithium pack. The unit is running perfect on the UPS output without AC present. The moment you introduce AC. The Output Earth Leakage trips. I have separated the neutrals(Eskom and Inverter) and we having this issue. Eskom loads and Inverter loads have earth Leakage.
October 20, 20214 yr Make sure the inverters grid in/non essential is fed from before the main earth leakage and not after.
October 20, 20214 yr Author 4 hours ago, PowerUser said: Do you have the Earth - Neutral bond relay connected to the inverter? Earth and nuetral bond is on the Eskom side
October 20, 20214 yr Author 4 hours ago, Nexuss said: Make sure the inverters grid in/non essential is fed from before the main earth leakage and not after. Noted will try it out over the weekend and report back
October 20, 20214 yr 16 minutes ago, Thee Mister EX said: Earth and nuetral bond is on the Eskom side You need another Earth - Neutral bond on the inverter as per the manual: Search around the forum. Your issue has been discussed multiple times... Edited October 20, 20214 yr by PowerUser