Gerrie Posted November 10, 2021 Posted November 10, 2021 I’m trying to find allowable COCT Grid charging current for 5KW and 8KW grid tie systems, does anybody have the allowable current? Quote
0 Tariq Posted November 10, 2021 Posted November 10, 2021 It is 25% of your grid connection ( as far as I understand the rules ), eg. 15 amps for a single phase 60 amp grid supply Gerrie 1 Quote
Question
Gerrie
I’m trying to find allowable COCT Grid charging current for 5KW and 8KW grid tie systems, does anybody have the allowable current?