Wire guage for Pylontech US3000 batteries with 10kW system

Featured Replies

We currently have 4x Narada 12V-200ah gel batteries connected in series with Infini 10KW hybrid inverter. Planning on swapping out gel batteries with 2X Pylontech US3000. Currently we have a very thick wire (probably 2 AWG) to handle massive amps (200A) that inverter can pull from the battery bank. 

However, all the videos I'm seeing online have pylontech batteries seem to be connected in series via much thinner cables (see video below). Can someone clarify how is the voltage not increased when batteries are connected in series, since a battery is already 48V? and how are those thin cables able to handle large amount of amps?

 

 

 

 

Edited by LionKing

  • LionKing changed the title to Wire guage for Pylontech US3000 batteries with 10kW system

Those batteries in the video are connected in parallel. Series would have +ve connected to the next -ve. 

As for cable thickness, the Pylon cables are rated for 125A which should be more than enough for 2 x US3000 batteries. For more power, you can simply double up on the cables.

Edited by Froggie

  • Author
1 minute ago, P1000 said:

2xUS3000 Batteries will only be able to supply 3552W. (37A*48V*2).

Yes, I realized after I asked the question. I'd have to go with UP5000 then. Any idea why UP5000 is not on pylontech's website? Is it an older/discontinued model?

  • Author
1 hour ago, Froggie said:

Those batteries in the video are connected in parallel. Series would have +ve connected to the next -ve. 

As for cable thickness, the Pylon cables are rated for 125A which should be more than enough for 2 x US3000 batteries. For more power, you can simply double up on the cables.

Ah, I just noticed. About the cable thickness, the guy in the video below has UP5000 batteries daisy chained (parallel?) in what appears to be groups of 4, do these cables look thick enough to push 200+ amps?

 

6 minutes ago, LionKing said:

Ah, I just noticed. About the cable thickness, the guy in the video below has UP5000 batteries daisy chained (parallel?) in what appears to be groups of 4, do these cables look thick enough to push 200+ amps?

 

2xUP5000 will only do 4800W (total) sustained.

Don't overthink the wire sizes between the batteries. Those are rated for 120A, but in the case where you need more than 5kW from your bank, you have to connect the inverter to both ends of the bank:

Screenshot_20210725-125451_Acrobat for Samsung.jpg

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.