September 2, 20224 yr Hi Guy's, Please assist. I am installing a Kodak 7.2 inverter. The manual calls for us to use a 10mm (Gauge 8 )Ac input cable. I understand that a 60A breaker should be used on the AC input and output cables. Segen posted a recommendation that we should use a 40A QA!# Circuit Breaker Curve 3. This is to protect the inverter from large loads. Now I don't know what size breaker I should be using? Please assist.
September 2, 20224 yr 53 minutes ago, Steve 69 said: Now I don't know what size breaker I should be using? Breakers are sized to protect the wire. Eg if a wire is rated for 44A.... you should not use anything greater than a 40A Breaker. There are SANS tables that specify the current rating If your breaker rating is larger than the wire and you pull a load that is still below the breaker value then the wire will heat up and cause a fire and the breaker will never disconnect the load.
September 2, 20224 yr 22 minutes ago, iiznh said: Breakers are sized to protect the wire. That is 100% correct! Too many peoples (even engineers) believe they can protect equipment with breakers or fuses. For the protection of motors and transformers exist a specific line and type of protective devices, on witch one can set the current limit according to the equipment rated current. Such devices have a different thermal heating characteristic than wires. Therefor the Axpert line of inverters have their own protective device built in.