Battery settings on Sunsynk for Pylontech UP5000

Featured Replies

  • Author
4 hours ago, Tinbum said:

You shouldn't have to change any if you have the communication set up correctly already, just put the newest as master.

I am not to sure if it is correct. This is how it currently is.

20220920_060947.jpg

20220920_060959.jpg

20220920_061038.jpg

20220920_061045.jpg

20220920_061102.jpg

1 hour ago, Adriaanvt said:

How should they be ?

On the first battery nr 1 is up. 

2nd and 3rd all down

Ok, that should not really make a difference, but ideally they should be the same on all the batteries:

image.png.90be59b6c87073c8f9f7b1698478d4fd.png

You have to restart the battery for that change to take effect.

Edited by P1000

  • Author
4 minutes ago, P1000 said:

Ok, that should not really make a difference, but ideally they should be the same on all the batteries:

image.png.90be59b6c87073c8f9f7b1698478d4fd.png

You have to restart the battery for that change to take effect.

Thank you, will change them later when I get home.

You are using CAN communication so all the DIP switches should be OFF. (up)

Your voltage settings are all wrong and dangerously wrong- your batteries will be damaged and require new BMS's. DO NOT leave it on with these settings.

The settings should come via the CAN from the battery so it looks as if that is not working. Make sure pins 1-3 are not connected at all and you are using 4 and 5 (all at the battery end). For the inverter end look in your manual

Edited by Tinbum

15 hours ago, Adriaanvt said:

Hi there

I had 2 pylontech up5000 batteries in the system and just added a third. 

What battery settings should I change ?

3 x 2 pylontech up5000 batteries
3 x 4.8kWh
Recommended charge/discharge current is 50A per battery.
Which model SunSynk inverter do you have?

You have 100A charge / discharge limit
100A * 48V = 4.8kW
If you have the 8kW inverter, you could use 150A * 48V = 7.2kW to prevent clipping.

As per SunSynk manual, check LiBMS screen to ensure that the inverter & battery are communicating.
The Voltage Settings are ignored if LiBMS is communicating, but best to set them as per Pylontech recommendations of 53.5V
Also set 90 days to zero as conditioning is done by the BMS.
The shutdown 20% needs to be set with System Mode 1 in mind.
On mine, I have System Mode 1 of 20% and shutdown of 5%

Edited by system32

  • Author
4 minutes ago, system32 said:

3 x 2 pylontech up5000 batteries
3 x 4.8kWh
Recommended charge/discharge current is 50A per battery.
Which model SunSynk inverter do you have.

You have 100A charge / discharge limit
100A * 48V = 4.8kW
If you have the 8kW inverter, you could use 150A * 48V = 7.2kW to prevent clipping.

As per SunSynk manual, check LiBMS to ensure that the inverter & battery are communicating.
The Voltage Settings are ignored if LiBMS is communicating, but best to set them as per Pylontech recommendations.
Also set 90 days to zero as conditioning is done by the BMS.
The shutdown 20% needs to be set with System Mode 1 in mind.
On mine, I have System Mode 1 of 20% and shutdown of 5%

Good day

I have a 5kw inverter. My system mode one is at 50%. 

48 minutes ago, Adriaanvt said:

Good day

I have a 5kw inverter. My system mode one is at 50%. 

With a 5kW inverter,
Discharge/charge of 100A * 48V = 4.8kW is correct.
According to the manual, the UP5000 is

  • Nominal Capacity (Wh) 4800 * 3 = 14.4kWh
  • Usable Capacity (Wh) 4560  * 3 = 13.68kWh
  • With 95% DoD (== 5% SoC)

With SoC 50% System Mode 1, means you will use 50% of 14.4kWh = 7.2kWh of the battery at night.
The inverter will shutdown if the SoC drops below 20%.
During night time & load shedding & battery at 50% you will sill be able to use from 50% -> 20% => 4.32kWh.
4.32kWh is the minimum, if the battery was at 60%SoC, then you will have from 60% -> 20% SoC.
The SoC 50%/20% is conservative (and probably good for stage 6).
I would use a shutdown SoC of 5% or 7%.
I would then consider also dropping the System Mode 1 lower.
I use a more aggressive 20%/5%, which means that I discharge my battery to 20% SoC daily which for Lithium batteries should be OK.
[Most nights I have 28-40% SoC still left unless it rained the day before]

The SoC 50%/20% is also dependent on the total battery capacity - you have 14.4kWh which is quite large.
A 20%/5% or 30%/10% will save more grid.

Edited by system32

  • 1 year later...

Hi, Its Bilal Ahmad have Three Inverex (8+8+8kw) nitrox Invertors, And Three Batteries Parallel of (pylonthic Lithium up5000x3)

,

Use Battery= ? lithium Or Battery Volt OR Batta %.  ??

(What i Have to Select)?

Capacity= ?

Max Amp charge= ?

Max Amp Discharge= ?

What will Be The Float v = ?

Absorption v = ?

Equalization V = ?

 

My WhatsApp No. is

+923038949403

 

 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.