May 12, 20233 yr Hello Smart Peeps, Setup: 8x 550w panels, 8kw Deye Inv, 2x shoto 5.12kwh Setup installed by solaradvice. I noticed that during loadshedding, the consumption indicator \ reading is spot on, but when the grid is on, the consumption shows 0? Any ideas? Zero export to CT ticket. Many thanks!
May 12, 20233 yr !st answer everyone is going to give is a question... Is the CT coil 100% correctly installed, wired and oriented? 99% or reading errors or discrepancies on these inverters are usually related to the CT coil not being correctly installed.
May 12, 20233 yr Author Thanks for the quick reply. I have no idea even what the CT looks like, But I will mention this to my installers. Any other 8kw Deye users out there with the same setup? maybe we can compare settings and setup. I assume it’s this part: