June 1, 20233 yr Hi All I have a question around using JA Solar and Longi Panels on my Low voltage Axpert inverter. I currently have 2 * 555W Longi panels and would like to add 2 or 4 more JA solar 550W. I have compared the stats and they are very very close (see below), if I add the JA Solar in an additional string (or two) would I have any performance degradation? The reason for this it that I can get the JA Solar panels for about R400 a panel cheaper (got the Longi's from a fellow power forum user). JA Solar Longi Rated Maxium Power [W] 550 555 Open Circuit Voltage [V] 49,9 49,95 Maximum Power Voltage[V] 41,96 42,1 Short Circuit Current [A] 14 14,1 Maximum Power Current [A] 13,11 13,19 Module Efficiency [%] 21,3 21,5
June 1, 20233 yr 2 hours ago, uDuWaR said: Hi All I have a question around using JA Solar and Longi Panels on my Low voltage Axpert inverter. I currently have 2 * 555W Longi panels and would like to add 2 or 4 more JA solar 550W. I have compared the stats and they are very very close (see below), if I add the JA Solar in an additional string (or two) would I have any performance degradation? The reason for this it that I can get the JA Solar panels for about R400 a panel cheaper (got the Longi's from a fellow power forum user). JA Solar Longi Rated Maxium Power [W] 550 555 Open Circuit Voltage [V] 49,9 49,95 Maximum Power Voltage[V] 41,96 42,1 Short Circuit Current [A] 14 14,1 Maximum Power Current [A] 13,11 13,19 Module Efficiency [%] 21,3 21,5 No problem as long as each string have the same number of panels in the strings used in parallel.
June 1, 20233 yr 26 minutes ago, Scorp007 said: No problem as long as each string have the same number of panels in the strings used in parallel. 100%, If I can slightly expand on this, in essence: Each string similar Voltage as in Parallel V is determined by the smallest V. In your example: Adding two more strings of two panels each to your already single string of two panels in series ending with 2s3p Current setup: PV1 = (42.1 x 2) = 84.2V, Amps = 13.19A (Longi) PV2 &3 = (41.96 x 2) = 83.92V, Amps = 13.11A (JA Solar) PV1+2+3 = 83.92V, 39.41A = +/- 3307W At NOCT - Values should also be very close to very little loss. https://footprinthero.com/solar-panel-series-and-parallel-calculator Edited June 1, 20233 yr by Eurard
June 2, 20233 yr Author This is great thanks guys, Wow I was expecting a 1 to 3 % losses as acceptable but .2% is practically nothing. Now that it works I need to figure out mounting, but considering that the JA Solar is 2279mm * 1134mm and the Longi is 2278mm * 1134mm they are essentially the same size. I guess mounting holes can be drill if strictly necessary.
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.