Hi Guys 

I am trying to help one of my neighbors with their inverter settings and I have noticed that they appear to be exporting power to the grid

Sunsynk 12kw 3-phase inverters x 2 

If I go onto the Sunsynk Website to Grid I see the following 

image.thumb.png.9a2a51acaf35915fbbebc678dd1ada09.png

That looks like they are exporting 4kwh of power on that day. 

It looks like it is probably happening when their battery is full 

image.thumb.png.5273de35e051a91ea9451a9cb6cd31df.png

 

 

 

I have checked their system mode settings and they appear to be set correctly 

image.thumb.png.9858fc45f499ebdce06082307432b89c.png

So, my questions are: 

1. Am I reading correctly that their inverters are feeding back into the grid for some reason. 

2. If so, how do we stop it from doing that as it looks like the settings are set correctly for 0 feedback into the grid. 

Any ideas?

Link to comment
Share on other sites

Sunsynk updated the firmware but still feeding back into the grid.

Is now coming up with a F41 and W31 Parallel comms issues, they have spoken to the installer and they are going to come and sort it out. 

Looks like it has been an issue since the site was installed as they have been feeding back into the grid for the last 18 months. 

The comms between the inverters was not working properly before the update but it wasn't reporting any errors as you could change work mode settings on one inverter and it did not update the settings on the slave.  

 

image.thumb.png.a9e8efd9a4f8c0430d78b79957a122c4.png

Edited by Sc00bs
Link to comment
Share on other sites

Just now, Chunks said:

Hi Scoobs, 

I’ve assisted with a similar situation. The problem was the installation of the CT clamps are on the wrong phases. 

Thanks for that  @Chunks  appreciate it 🙂 

I will speak to their installer and suggest that they check that they have the phases setup correctly. 

Link to comment
Share on other sites

  • 2 weeks later...

@chunks , so the exporting of power has stopped. I am assuming that the installer changed the CT's as they were onsite and the feed back into the grid stopped. 

The inverters is however pulling power from the grid when it is not necessary. Yesterday for example, the batteries were @100% by 13:00 and PV production is throttled bac, there is still however a 500W load on the grid and that increases to 3.6kw @13:25 pretty much in time with the load increasing. 

Installer has said he thinks that there is some lightning damage and that the inverters need to be sent back to Sunsynk for repair. 

Just to confirm, there are 2 x 12kw Sunsynk inverters, wondering if this could could still be the Ct clamp issue.

image.thumb.png.5ca8fad21f9c9b8990f2cefc0d5a7023.png

image.png.f6c1f9bf5d654ac4d4ad90baa193be9f.png

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...