Sunsynk 3 x 16kw max 3 phase F26 bus unbalance fault

Featured Replies

Hi All,

i have a client with the following setup. They keep experiencing issues when its loadshedding , as soon as the power goes out, they get a F26 Bus unbalanced fault on the master modbus 01 inverter. Then they loose power over all 3 phases because of the on inverter that died. We have checked the PV for earth leakage, we checked the lightning arrestors. Changed them aswell, with no luck. They only experience this when the PV side of things is low and there is no grid. Mabey once in 2 months. We are stuck on why this would happen, any help we will appreciate.

Phase A - Inverter 1 - Modbus 01

Phase B - Inverter 2 - Modbus 02

Phase C - Inverter 3 - Modbus 03

They all go to a common DC busbar.


Inverter 1 - with the fault codes load on the inverter.

image.png

Inverter 2

image.png

Inverter 3

image.png

Does this happen when you switch off the Eskom MCB, or only with loadshedding?

How close are the inverters together, and are you using the supplied comms cables?

All inverters on the same firmware version.

What batteries are on site, cable size and length?

3 hours ago, Divan Du Toit SST said:

They only experience this when the PV side of things is low and...

Most strange, because on change-over from grid to battery and PV, battery takes the instantaneous load, and then the MPPT's catch up if solar is available.

Does this also happen at night with no PV?

Has this fault occurred from installation, or is this something new?

Have you tried setting another inverter as master?

Just a few questions, then I'm sure everyone will jump in. 👍

Measure DC voltage and current at each inverter under load and compare. A significant drop at Inverter 1 suggests a bad connection or higher resistance on the DC cabling. This happens with low pv generation and no utility backup pointing to battery issue on inverter 1.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.