May 9, 20197 yr No on and off grid charging specs - set the voltages and that it. https://www.trojanbattery.com/pdf/Trojan_QSG_Flooded.pdf And https://www.trojanbattery.com/pdf/TrojanBattery_UsersGuide.pdf At what amperage do you charge? 15% of bank AH as charge current during load shedding. Otherwise 10% of AH as charge current is fine.
May 10, 20197 yr Author I have a 60 amp microcare mppt,it only has a bulk and float charge setting,i have the charge settings to data sheet,at 3pm it goes to float charge and i check the soc of the batteries and its not near fully charged but floats at 1.2 amps,the soc only goes to green after equalising batteries
May 10, 20197 yr 3 hours ago, [email protected] said: ... the soc only goes to green after equalising batteries ... Have a chat to Microcare?
May 10, 20197 yr You must check the time and the amperage settings that decide when the MPPT goes to float. I don't have the manual handy, but after the bulk charge when the amps drop below a level that you can set and stay there for a set time, then it goes to float. Your amp setting may be too high.
May 17, 20197 yr I have a similar setup and want to know what settings have you eventually used on the microcare MPPT ?
May 19, 20197 yr Author After i adjusted the bulk to float at 2hours and go to float if charge lower than 3amps its makes a huge difference,thanks very much