Balancing Mecer Axperts

Featured Replies

Hi all

 

New here i had a 10kw system installed earlier this year, 2x 5kw Mecer inverters 24 Panels, and 2 x (4x120ah) batery banks.

 

Since yesterday my two inverters dont balance the load between them properly i attached pictures.

 

Any assistance would be greatly appreciated

IMG-20191017-WA0052.jpg

IMG-20191017-WA0051.jpg

49 minutes ago, Gerrit1984 said:

Hi all

Welcome Gerrit

49 minutes ago, Gerrit1984 said:

and 2 x (4x120ah) batery banks.

I just want to make sure this is 2 parallel banks, or is it one connected to the one inverter and one connected to the second inverter?

49 minutes ago, Gerrit1984 said:

Since yesterday my two inverters dont balance the load between them properly i attached pictures.

During the time of the pictures the load was exceeding the capacity of your panels so it went into bypass mode (assumption), No 1 inverter was reporting an overload. I am not sure how Axperts divide load during "Bypass" mode, but maybe @Coulomb can assist in this regard. 

7 hours ago, Jaco de Jongh said:

I just want to make sure this is 2 parallel banks, or is it one connected to the one inverter and one connected to the second inverter?

Yes, this is important. Otherwise, strange things can happen, and there is a fault code if the inverter happens to detect it.

7 hours ago, Jaco de Jongh said:

the load was exceeding the capacity of your panels so it went into bypass mode (assumption),

It would be in bypass mode because the load exceeded 110% of the inverter capacity (5.5 kW), or possibly 100% of the capacity for a longer period of time.

7 hours ago, Jaco de Jongh said:

I am not sure how Axperts divide load during "Bypass" mode, but maybe @Coulomb can assist in this regard. 

When bypassing, AC-in is connected to AC-out via a relay. I suspect that you have a loose and/or high resistance connection to inverter 2, else the wiring should be sharing the load much more closely. In fact, 35 W is so low, I doubt that inverter two's output is connected at all.

The other possibility is that inverter 2's relay is damaged. But I'd check the wiring thoroughly first.

If you switch off inverter 1, does inverter 2 power the loads? Do this with a low but non-zero load; if the wiring is high resistance, a high load could cause the connection to heat up and even become a fire hazard. Check the AC wiring with a non-contact thermometer if you have one, especially at the terminal blocks of the inverter, breakers, etc. Neutral as well as active.

  • Author
On 2019/10/17 at 6:49 PM, Jaco de Jongh said:

Welcome Gerrit

I just want to make sure this is 2 parallel banks, or is it one connected to the one inverter and one connected to the second inverter?

Yes the banks are in Parallel

On 2019/10/18 at 2:15 AM, Coulomb said:

When bypassing, AC-in is connected to AC-out via a relay. I suspect that you have a loose and/or high resistance connection to inverter 2, else the wiring should be sharing the load much more closely. In fact, 35 W is so low, I doubt that inverter two's output is connected at all.

It was the fuse on the AC outlet that was burnt, the installer inserted 2 25A fuses instead of 32A. Replaced them and now the system is running balanced again. Than you all for the advise 

6 minutes ago, Gerrit1984 said:

It was the fuse on the AC outlet that was burnt, the installer inserted 2 25A fuses instead of 32A. Replaced them and now the system is running balanced again. Than you all for the advise 

Great, I am glad you are sorted.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.