14 hours ago, Alieu cama said:

bus soft started error [09] cause I mean what causes it

Fault code 09 is a well-known Axpert error code, relevant to all models that I know of.

When the inverter starts up, it slowly charges the bus capacitors (the "soft start") and reads the bus voltage. If the voltage doesn't rise enough in a certain time, fault code 09 results.

It could mean that the small power supply used to charge the bus capacitors is faulty, but sadly more often it means that IGBTs have shorted, either  in the inverter proper (the DC to AC converter), or at the bus end of the battery DC-DC converter.

If you're handy with electronics, there is some good information in the PIP inverter repairs and hardware modifications topic.

Link to comment
Share on other sites

  • 2 weeks later...

Hi to everyone I want to ask what causes error [5] for ultra power 1kva is always alarming error 5

On 2020/02/22 at 1:14 PM, stoic said:

Welcome @Alieu cama,

The experts on this forum will require a bit more info. To start off with, what inverter do you have? a picture of the sticker showing the details will be very helpful

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...