August 1, 20206 yr Hi, If my axpert inverter are in bypass mode (utility supplying the load) how much current can be transferred from utility to load in bypass mode. I am struggling to get any data. If I understand it correctly if it is a 5KVA inverter this is the power that can be delivered when in inverter mode. Thanks
August 2, 20206 yr 11 hours ago, Elroy said: how much current can be transferred from utility to load in bypass mode The relays are rated at 40 A, and there is a 40 A breaker at the AC-in connection. So roughly 40 A x 230 V = 9.2 kVA (depending on the Eskom voltage). Depending on your load power factor, that might be around 7.5 kW. Edit: that assumes that your cables are rated for 40 A, of course (6 mm²), if you want to pass that power continuously. With 4 mm² cable, you should limit to 30 A continuously for safety. 11 hours ago, Elroy said: If I understand it correctly if it is a 5KVA inverter this is the power that can be delivered when in inverter mode. Yes. Edited August 2, 20206 yr by Coulomb