Good day. 

Hope someone can give me advise, I've got a Axpert 5KVA inverter, with a 5.1Kwh Li-Ion Battery. The inverter runs 100% for about 6 days and then the solar side just stop charging, it show the PV sign but it does not give PV power. I just switch the inverter off and open my PV fuses and switch the inverter on again, then it runs again for about 6 days and then the problem is back. Any advise? Can it be a fault in the inverter? 

Link to comment
Share on other sites

2 hours ago, KAROOsolar said:

4 Strings of 3 panels. 

This is very likely to be the problem.  These inverters really need to be wired 2-in-series when using 72-cell panels like yours.  I had mine wired the same as yours and similar problems - changed to 2S6P and all now fine.

The only funny is the 6 days - that is probably a coincidence.

Link to comment
Share on other sites

Hey all

 

I did the 2s-2p and it didn't work. I had to pay more in on grid. so now I have it back to 3s1p and it works well. ok, I don't have 12 panels. I did the same panels at my parents house and it runs in a 3s2p with no problems. 

Link to comment
Share on other sites

2 hours ago, Barryv said:

ok, I don't have 12 panels.

It's quite possible that heat is a factor, and 12 panels would definitely generate more heat in the solar charge controller than 3 or 4.

Also, yours may be 60-cell panels. Those do need to be wired 3S. But 60-cell panels are much less common these days.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...