November 22, 20205 yr Do I need to run ground wire from each connector strip GRID, GEN and LOAD back to the db ground or is it ok to run a wire from chassis ground back to the db ground
November 22, 20205 yr Author So just clarifying, are you saying one wire from chassis ground to db ground Edited November 22, 20205 yr by Tariq
November 23, 20205 yr Author yes, i did do the continuity check, they are internally connected, looks like that is standard on most stuff
November 23, 20205 yr Where do we slot in the earth bonding relay. If GRID fails do we then bind do Neutral-Earth bond with the relay. Meaning LOAD neutral will be connect to the 3 neutral and the DB neutral from the GRID?
November 23, 20205 yr Author I am planning to connect the load neutral ONLY to one terminal of the relay and the chassis ground to the second terminal of the normally open relay, somebody please correct me if I am wrong