August 12, 20215 yr I have been following the discussions around prepaid meters tripping with grid export set to zero, and wondering if anyone has experience with the Conlog BEC23 ED? Is there a setting that prevents this? I see suggestions are up to 100W. Also, is there a difference in the CT clamp direction between Sunsynk and Deye - I have found contradicting advice on the internet.
August 21, 20215 yr Author For the record, the Conlog meter is OK with a setting of 150W for now. Will reduce at a later stage and monitor.
August 23, 20215 yr On 2021/08/12 at 11:52 AM, shovelhead said: is there a difference in the CT clamp direction between Sunsynk and Deye I don’t know the Deye CT but have just done the Sunsync CT. There is a arrow on the CT and the arrow needs to point in the direction of current flow from grid to the load-side.