Prepaid meter and Sunsynk/Deye inverter


shovelhead
 Share

Recommended Posts

I have been following the discussions around prepaid meters tripping with grid export set to zero, and wondering if anyone has experience with the Conlog BEC23 ED?  Is there a setting that prevents this?  I see suggestions are up to 100W.

Also, is there a difference in the CT clamp direction between Sunsynk and Deye - I have found contradicting advice on the internet.

Link to comment
Share on other sites

  • 2 weeks later...
On 2021/08/12 at 11:52 AM, shovelhead said:

is there a difference in the CT clamp direction between Sunsynk and Deye

I don’t know the Deye  CT but have just done the Sunsync CT. There is a arrow on the CT and the arrow needs to point in the direction of current flow from grid to the load-side.