shovelhead Posted August 12, 2021 Share Posted August 12, 2021 I have been following the discussions around prepaid meters tripping with grid export set to zero, and wondering if anyone has experience with the Conlog BEC23 ED? Is there a setting that prevents this? I see suggestions are up to 100W. Also, is there a difference in the CT clamp direction between Sunsynk and Deye - I have found contradicting advice on the internet. Quote Link to comment Share on other sites More sharing options...
shovelhead Posted August 21, 2021 Author Share Posted August 21, 2021 For the record, the Conlog meter is OK with a setting of 150W for now. Will reduce at a later stage and monitor. Quote Link to comment Share on other sites More sharing options...
Gerrie Posted August 23, 2021 Share Posted August 23, 2021 On 2021/08/12 at 11:52 AM, shovelhead said: is there a difference in the CT clamp direction between Sunsynk and Deye I don’t know the Deye CT but have just done the Sunsync CT. There is a arrow on the CT and the arrow needs to point in the direction of current flow from grid to the load-side. Quote Link to comment Share on other sites More sharing options...