Different brands in a bank
Huawei charging voltage 53.5 Narada charging voltage 54.v Huawei discharge cutout 44v Narada discharge cutout 40v Both same battery chemistry
- Different brands in a bank
-
Different brands in a bank
Quick Question and advise needed. Customer has 1x 48v Huawei 100amp (4.8kwh) battery feeding a cloned 5kva axpert jobbie from the sun pays. After checking specs the battery BMS is limited to 50amp output only, Battery routinely cuts power to inverter above 50amp draw, Now I can't find these for sale lately, Can I add a Narada 100amp 48v lithium to the current setup with known 100amp output? Anything to watch out for? (Besides the clone) Thanks in Advance From NF N
-
Best string config Axpert MKS-II 450V MPPT
Would suggest 2 strings of 6panels to get 240vdc +- way withing the inverters MPPT range of 120v ~ 450v Total of 4800w with bit left for "play" Would suggest 6 panels towards sun up And 6 sundown position for maximum on solar load time. But the Mark11 also run well with 4 panels together for 160w with first hand exsperiance runnings pool pumps ect. All is your load profile and Battery size dependent.