Posted November 21, 20213 yr Good day I need advice/help/support I installed a Sunsynk 8kw inverter. the CT coil is correctly installed and does show my watts used and it is positive so the direction is correct. but I do not push any solar power in to the non essensial load only use the grid? The inverter also trip my earth leakage ? What am I doing wrong please thank you
November 21, 20213 yr 6 hours ago, Blue Bull said: The inverter also trip my earth leakage ? Is your inverter fed from before or after the earth leakage? if it’s after the earth leakage it could be the reason why it’s tripping.
November 21, 20213 yr Have you ticked “ limit to load “ on your System Mode screen, if so, unstick it
November 21, 20213 yr Author 1 hour ago, Tariq said: Have you ticked “ limit to load “ on your System Mode screen, if so, unstick it Wow thank you I umstick is and wow the ct coil is displayed and yesss it actually work! only thing it is now using battery as the sun is about gone. I assume it needs to be sorted on the time table? My CT watt is + LD: is neg watt I think this is fine last Q I put ct coil on neutral wire with arrow pointing away from mains grid input. Wow I do appreciate your support!!!
November 21, 20213 yr 38 minutes ago, Blue Bull said: only thing it is now using battery as the sun is about gone. I assume it needs to be sorted on the time table? Yes the times, percentages and maximum watt can be set so that you don’t discharge batteries all the way. It’s better to leave some power in the battery in the event of load shedding. If you don’t get this setting right you might end up with a drained battery when load shedding starts.
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.