mzezman Posted March 21, 2022 Share Posted March 21, 2022 How critical is an E-N bond on the SS 5 / 8kw? My installer didn't put one in and on other forums there are installs without one but also with no issues in months / years. Is this something that must be mandatory? Quote Link to comment Share on other sites More sharing options...
phidz Posted March 21, 2022 Share Posted March 21, 2022 I put E-N bond on mine because when the grid was down, some led lights would remain on (faintly)even if the switch was off. mzezman 1 Quote Link to comment Share on other sites More sharing options...
P1000 Posted March 22, 2022 Share Posted March 22, 2022 How critical is it to have earth leakage protection? Is it mandatory? Off course it is. Without a neutral-earth bond, your RCD will not work (when islanded). mzezman 1 Quote Link to comment Share on other sites More sharing options...
mzezman Posted March 22, 2022 Author Share Posted March 22, 2022 Great - thank you -so need to cal out installer again to get this done Quote Link to comment Share on other sites More sharing options...