Axpert Parallel System - Different load in Grid mode

Featured Replies

Hi PowerForum Users,

Looking for some assistance into a problem being experienced in a single phase parallel Axpert power system. 

3 x Axpert 5kVA/4kW inverters setup in parallel.

We have the communication cables and current sharing cables installed, and have tried to ensure that the AC input cables and AC output cables are equal length.

While the Axpert inverters are in Grid mode, their respective load power can differ quite significantly – to the extent that the system has been tripping one of the inverters recently. 
However, while the inverters are in SBU mode, the load is shared very equally across all three inverters and an overload event has not been experienced. 

Here is a screenshot of the different load being observed by each inverter while in Grid mode:

1335669524_JDG3xAxpert5kVAParallel.jpg.bef312ada8bd5cb52020bbc7e322733f.jpg

 

Looking for any insight into how to remedy the problem.

 

Thanks in advance,
Nicholas

Since they share well in battery mode, I'd say that the output cabling is fine. 

Since they don't share in grid mode, which for your models means bypass mode, it looks like the problem is with the input wiring, or the internals of at least two machines (e.g. high resistance relay contacts, loose wires or terminals, etc).

I think it could possibly be some sort of neutral or earth weirdness, but I can't put my finger on it right now. 

When in grid mode with a significant load, it would be worth checking that the voltage at the three AC-in terminals is very similar. 

Edited by Coulomb

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.