Good day all

Recently purchased a brand new Mecer 2400va invertor, and been set up complete with 2 x 12v batteries

As of today Eskom went off and invertor switched to battery mode however the load, a basic home office setup didnt come on

Prior to this it had worked

Panel shows output of 224, no error or fault messages

Tried pressing reset switch to no change

Please help, thanks 

20220420_200756.jpg

Posted

thanks, i have pressed that countless times to no change, also the output reads as per screen however when on battery nothing is powered at all

hope that makes sense

 

Posted
4 minutes ago, LyricalYC said:

thanks, i have pressed that countless times to no change, also the output reads as per screen however when on battery nothing is powered at all

hope that makes sense

 

I would remove the lead connected in the sockets feeding the loads and connect only a cell charger in the one socket. Check if the charger is working. Do this when the grid is on as well as when you switch off the plug feeding the unit.

See if charger works both ways to charge phone.

Posted
17 hours ago, Scorp007 said:

Thank you, i used a desk lamp and it powers up when invertor is connected to grid and as soon as grid powers off it switches off although the panel still shows output

 

Posted
4 hours ago, LyricalYC said:

 

The guys that know the circuit for your inverter might give their ideas why panel is on but no output.

As it is new have it checked out and repaired instead of fiddling around and battling with a faulty unit.

Posted
23 hours ago, Scorp007 said:

As it is new have it checked out and repaired

Presuming that it's a genuine Mecer (and that the Mecer is a genuine Voltronic UPS, or some other reasonable brand), yes. You presumably paid more for the warranty support (compared to a clone direct from China, say).

I believe that Mecer have decent repair centres too, for when it's out of warranty.

Posted (edited)
10 minutes ago, Coulomb said:

Presuming that it's a genuine Mecer (and that the Mecer is a genuine Voltronic UPS, or some other reasonable brand), yes. You presumably paid more for the warranty support (compared to a clone direct from China, say).

I believe that Mecer have decent repair centres too, for when it's out of warranty.

The worst clone we were talking about some time ago with less than 15 settings packed up with some smoke within a few weeks and he managed to have it repaired by the seller. It has been running OK now for about 4 months. This does prove when buying from a seller with a workshop does help when venturing into the clone mine field.

The picture in this case seems like a Mecer sold as a combo unit.

Edited by Scorp007
Posted

thank you all, it is a genuine Mecer unit, challenge it will cost nearly same to ship it back to supplier as unit was sent out of country

i have however concluded the breaker is faulty, non responsive and would like to replace it.

where can i source an L2 series 2 ups 15a breaker, i seem to be landing on 20A or 50A ones however want to try replace with exact one on faulty unit (see pictures)

either an online store or physical store in Joburg West area will do

 

Thank you

 

l2 series.jpg

WhatsApp Image 2022-04-24 at 11.48.37 AM.jpeg

Posted
2 hours ago, LyricalYC said:

thank you all, it is a genuine Mecer unit, challenge it will cost nearly same to ship it back to supplier as unit was sent out of country

i have however concluded the breaker is faulty, non responsive and would like to replace it.

where can i source an L2 series 2 ups 15a breaker, i seem to be landing on 20A or 50A ones however want to try replace with exact one on faulty unit (see pictures)

either an online store or physical store in Joburg West area will do

 

Thank you

 

l2 series.jpg

WhatsApp Image 2022-04-24 at 11.48.37 AM.jpeg

https://za.rs-online.com/web/p/thermal-breakers/3445333

  • 7 months later...
Posted

Hi there have the same unit and it is completely dead, have connected the batteries and plugged it in but when i press the power on button nothing happens??

Posted
19 hours ago, HeinC said:

Hi there have the same unit and it is completely dead, have connected the batteries and plugged it in but when i press the power on button nothing happens??

Have you checked that the overload button on the left is not in a tripped state. Press it before switching on.

 

 

  • 3 weeks later...
Posted
On 2022/04/26 at 8:50 AM, LyricalYC said:

thank you

Hi I have exact same inverter with the same problem just wanted to find out after changing than breaker was the issue resolved

  • 4 months later...
Posted
On 2022/04/21 at 5:01 PM, chrisc said:

There is a circuit-breaker at the rear.  Push it in

Check the output with a meter

Hi, is the circuit breaker button like one in a DB for example? I have the Mercer 1200VA inverter. The battery only last an hour if we are lucky. Only 1 tv with the DSTV connected. Is the CB Button suppose to be clicking or hard to press in. At the moment nothing happens when I press it. How do you check the output (what rype of meter)? We purchased the Inverter in December 2022. Thank you

  • 1 month later...
Posted

Hey guys, 

I have a Mecer Lobo 1200va inverter. 

So everything is connected fine with battery and also plugged into the wall socket the unit is dead. 

Screen and warning lights does not come on and nothing happens. 

When I play with the power button and push it a few times the screen sometimes come on but like for a split second, flashes and off again. 

Any ideas on what could be the problem? 

Posted
23 hours ago, Yashin said:

Any ideas on what could be the problem? 

It sounds like the internal power supply is not working.

If it's several years old, it might be possible to replace a few capacitors and get it going.

23 hours ago, Yashin said:

fine with battery

How confident are you of the battery's health? Can you put a multimeter on it and report the voltage before and after switching on? Especially one of the times it comes on a little.

  • 7 months later...
Posted

Hi My Mercer 720w inverter charges battery when power switched of it displays a output voltage of 235v (AC) and the Battery displays 100% with orange led on but there is no output voltage on the sockets.I tested the circuit breaker it test  good on continuity(Note this CB is for AC supply incomer not to reset battery output voltage). Note when switching off the supply power there is a click sound from the relays and the machine changes over from standby to inverter mode. with no voltage when measured and the outlet sockets on the unit. What could be possible causes to this if possible a schematic diagram of the circuit would help. 

  • 1 year later...

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...