May 16, 20224 yr Hy Guys, I am trying to set up my BMS but the inverter is not communicating with the batteries. I have a 8kW inverter with 2 US 3000 batteries. I have tried the settings in both manuals. I have switched the batteries on and off and now the SOC is not displaying correctly. It was on 70% but now it is showing 100%
May 17, 20224 yr 18 hours ago, FrancoisFrundt said: Hy Guys, I am trying to set up my BMS but the inverter is not communicating with the batteries. I have a 8kW inverter with 2 US 3000 batteries. I have tried the settings in both manuals. I have switched the batteries on and off and now the SOC is not displaying correctly. It was on 70% but now it is showing 100% Have you used the correct cable from the batteries to Sunsynk? Used the right DIP settings on the batteries?
May 17, 20224 yr 18 hours ago, FrancoisFrundt said: Hy Guys, I am trying to set up my BMS but the inverter is not communicating with the batteries. I have a 8kW inverter with 2 US 3000 batteries. I have tried the settings in both manuals. I have switched the batteries on and off and now the SOC is not displaying correctly. It was on 70% but now it is showing 100% Send some pics of the inverter battery settings and LiBMS screen. See this thread from today , your settings should look the same. Edited May 17, 20224 yr by Nexuss
May 20, 20224 yr Author On 2022/05/17 at 2:10 PM, Scorp007 said: Have you used the correct cable from the batteries to Sunsynk? Used the right DIP settings on the batteries? It is the cable that came with the batteries. I saw that the cable is different for the 3000 and 3000c. How would I know if it is correct? dip switch settings 0000
May 20, 20224 yr Author On 2022/05/17 at 2:21 PM, Nexuss said: Send some pics of the inverter battery settings and LiBMS screen. See this thread from today , your settings should look the same.
May 20, 20224 yr Your BMS comms is not working if the LiBMS screen looks like that . I see it looks like you have the US3000B? I am not sure how the settings for those work but it should say in the manual.
May 20, 20224 yr Author Thanks, It just says US3000 on the battery so I suppose it could be a B. I have tried the settings in the manual but no luck. I suspect it is the cable. I have found this document. Will test the cable and see. Sunsynk Hybrid Inverters with lithium-ion batteries v3.pdf
March 8, 20233 yr Hi there. Did you manage to fix this? I have the same issue with my 8kw sunsynk inverter and 2x5kw batteries
March 9, 20233 yr Author Hi! Yes I did. I just changed the cable and then it worked. I switched the batteries off changed the cable to a standard RJ45 ethernet cable and it worked.
March 9, 20233 yr Standard RJ45 won't work for @Jameel Fakee. Jameel you haven't mentioned what battery manufacturer; almost certain though you'll need a certain RJ45 cable (or you could crimp one yourself based in pinout diagrams in inverter and battery)
March 17, 20233 yr I can not get the battery communicate saw a instruction pdf online from .. solar supplies, they say connect the yellow cable on the can port on the battery and BMS/CAN on the inverter and only dip switch 1 in on position everything else OFF. I have done that but it does not work, even reset the inverter to factory settings I tried a different R45 cable same result, even measured RJ45cables with tester, both cables are standard RJ45. Can anyone tell me if the yellow cable suppled does work or where I am going wrong please. Thank You Christoph SUNSYNK-PYLONTECH-WRITE-UP-12 battery connection setup 16032023.docx
March 17, 20233 yr I suspect thats the issue - the US3000C uses a different cable compared to the older US3000s (different pin-outs). You'll need to crimp a new plug on according to correct pin outs (steps have been discussed in other threads) or buy the appropriate cable.