Sc00bs Posted June 29, 2022 Share Posted June 29, 2022 Hi Guys I have a number of appliances in my house (vacuum cleaner for example) that cause the earth leakage to trip when we run them during load shedding. They however run just fine when we are grid attached and don't trip the earth leakage. Anyone have any ideas what could be causing this? Quote Link to comment Share on other sites More sharing options...
P1000 Posted June 29, 2022 Share Posted June 29, 2022 34 minutes ago, Sc00bs said: Hi Guys I have a number of appliances in my house (vacuum cleaner for example) that cause the earth leakage to trip when we run them during load shedding. They however run just fine when we are grid attached and don't trip the earth leakage. Anyone have any ideas what could be causing this? Are you sure all your neutrals are split correctly? Do you have a plug tester that you can use to check the threshold in both cases? Supergeek 1 Quote Link to comment Share on other sites More sharing options...
Jacques Ester Posted June 29, 2022 Share Posted June 29, 2022 Type of inverter and is there a Neutral/Earth bond relay installed. Supergeek 1 Quote Link to comment Share on other sites More sharing options...
Sc00bs Posted June 29, 2022 Author Share Posted June 29, 2022 Sunsynk 8kw It does have neutral/earth bonding but it is not using a relay, so I assume that the installer just put a jumper in somewhere to bridge the Earth/Netral as they had to come back once I worked out that it had a floating neutral. Sounds like the prime suspect is something to do with the Earth/Neutral bond Quote Link to comment Share on other sites More sharing options...
Nexuss Posted June 29, 2022 Share Posted June 29, 2022 11 minutes ago, Sc00bs said: Sunsynk 8kw It does have neutral/earth bonding but it is not using a relay, so I assume that the installer just put a jumper in somewhere to bridge the Earth/Netral as they had to come back once I worked out that it had a floating neutral. Sounds like the prime suspect is something to do with the Earth/Neutral bond Yea you are not supposed to do it like that you have to use a relay /ATS240. You will definitely get lots of nuisance tripping with it hard bonded like that. Quote Link to comment Share on other sites More sharing options...
Sc00bs Posted June 29, 2022 Author Share Posted June 29, 2022 Checked when running on battery with a plug and all the plugs report 100% with 2 lights shining, so Earth/Neutral are bonded. Quote Link to comment Share on other sites More sharing options...
Sc00bs Posted June 29, 2022 Author Share Posted June 29, 2022 1 hour ago, Nexuss said: Yea you are not supposed to do it like that you have to use a relay /ATS240. You will definitely get lots of nuisance tripping with it hard bonded like that. Ok, will speak to my installer then Quote Link to comment Share on other sites More sharing options...