Having issues, need some advice
3 minutes ago, P1000 said:
No, wave detection only relates to the time it will take to detect grid loss. The other features are not affected.
OK. So it comes down to what Goodwe mean when they say "fast", because a surge doesn't need to last/be allowed through for very long to do damage.
The inverter will never be able to protect from a surge, well it has MOVs or TVSs, but no software will protect from a surge. It can protect against over/under voltage events, but not very fast. The software needs to be able to measure the event, but more importantly, the relays need to switch, and they need to magnetize/demagnetize and that takes time - usually more than 1ms in the best case. The wave detection AFAIK only affects UPS operation - whether it takes 10ms, 20ms or (some longer period).
On 2022/09/09 at 10:31 AM, Bobster. said:
One thing to check is the safety code setting on the inverter. This is displayed in the PV master app and can be changed there. It should be set for South Africa. It then expects 230V plus or minus a bit, and will disconnect when the supply voltage gets too high or too low. When it disconnects, your backed up circuits will get a nice 230V (+- a smidgen) at 50Hz, but your non-backed up circuits will still get whatever is on the grid.
What is "too high" or "too low"?
It turns out that these are configurable via PV master.
Advanced settings ->Customer Safety Parameters -> Connection Parameters
you will see Upper Voltage & Lower Voltage settings.
These are first set by the safety code
Safety code = 50Hz default, Upper = 269, Lower = 171
Safety code = SA, Upper = 251, Lower = 197.5
But once you have set the safety code, you may override those settings.
Edited by Bobster.
Sppeling. Punctuation!!!!!!
So just an update. COJ did fix the local transformer and the voltage into my home dropped from the 250 to 258V range down to 230 to 240V. Since then things have been quieter with no additional loss. Hopefully its at an end now. An electrician I had out to do some work indicated after me relating the story that because my home was closest to the transformer in the complex I could expect worse damage than units deeper in the complex for surges in particular. So hopefully all is good now.
  • 3 years later...