Sunsynk Inverter Settings - Zero Export


Anton vD

Recommended Posts

, I got a 8kw Sunsynk Inverter installed, but if zero export is selected, so that we power the non-essential load also from solar/battery if eskom is on, the reading on the inverter go hywire. Getting zero load figures and pv figures also go up and down and grid go to negative. Sure this is not right. Is this a problem with the ct install or other settings that is wrong?

Screenshot_20230306_152543_Sunsynk Connect.jpg

Screenshot_20230306_152405_Sunsynk Connect.jpg

Link to comment
Share on other sites

Maybe post a photo of the ct coil installed. (forum people will quickly tell you if it's correct or not :)
It should ideally be right at your meter on the live wire. before it gets to the db.

Also the direction and also the polarity where the ct is connected to the inverter needs to be correct.

Weird jumping readings often points to incorrect CT coil setup.

Link to comment