Good morning all

I have  12 solar panels 450watt each connected in 3 strings

1 string has 4 solar panels

2 string has 2 panels

3 string has 6 panels

All are connected in parallel 

This is the only way I can connect up the panels due to the place there are and I can not move them.

The 3 strings go to a  combiner box which goes to my Voltonic 7200w inverter. Which charges up 6 x  US2000 lithium batteries 

My question is what is the best setup to get the most power for the panels would it help if I had a string in series 

Do all your panels have the same orientation or do they all face different directions?

Even if you can't move the panels, you would be better off with 2 strings of 6 panels each, i.e. to connect the 4 panel string in series with the 2 panel string and then parallel your 2 strings with 6 panels each.

2 minutes ago, jason compo said:

Would you be so kind as to show me on a diagram what you mean. And what would be the size of the fuse I need for the combiner box on the series and parallel string

A photo of your available roof space or a diagraM of your roofspace would help us give more accurate answers to your question :)

Does your Inverter have a single MPPT or 2 MPPT?
My recommendation would be that you string the top 6 panels in series (marked in red), and the bottom 6 in series (marked in yellow), but I believe you have those in series already.
Then feed one string into MPPT 1 and the second string into MPPT, if your Inverter does have 2 MPPTs.
If not, then you should parallel the two strings into the single MPPT. 
image.png.04bc2140e193e8756efdd1437be93e00.png

On 2023/04/13 at 10:07 AM, jason compo said:

Good morning all

I have  12 solar panels 450watt each connected in 3 strings

1 string has 4 solar panels

2 string has 2 panels

3 string has 6 panels

All are connected in parallel 

This is the only way I can connect up the panels due to the place there are and I can not move them.

The 3 strings go to a  combiner box which goes to my Voltonic 7200w inverter. Which charges up 6 x  US2000 lithium batteries 

My question is what is the best setup to get the most power for the panels would it help if I had a string in series 

Self deleted. 

Edited by Scorp007

So your Inverter has two MPPTs, meaning that you could couple each string independently to the Inverter if you wire your strings into  2 X 6Panel series strings.
 

  • Author
Just now, zsde said:

So your Inverter has two MPPTs, meaning that you could couple each string independently to the Inverter if you wire your strings into  2 X 6Panel series strings.
 

As I have said twice I have a combiner box so what do I have to do ?

1 hour ago, jason compo said:

As I have said twice I have a combiner box so what do I have to do ?

Based on my sketch you can remove say 2 fuses for the string of 2 panels and fit a 2nd SPD as I see you only have one fitted. Better to have each input to MPPT on its own SPD. 

4 minutes ago, jason compo said:

Southern Portugal  the system is pointing south

Ok that makes a lot of sense, I was confused there for a minute 😂

I can't help you with the other questions sorry. I'm not comfortable (or capable, to be honest) to give advice in this case, other than I think you need to get an installer or engineer out to assess and assist.

  • Author
1 minute ago, suds7162 said:

Ok that makes a lot of sense, I was confused there for a minute 😂

I can't help you with the other questions sorry. I'm not comfortable (or capable, to be honest) to give advice in this case, other than I think you need to get an installer or engineer out to assess and assist.

My system is installed and working perfectly and has been for about a year I just want to get more power out.

I do not understand why you have put fuses into the sketch but do not know what size fuse to put in

.so i just put in any  size fuse??