Growatt SPF 5000ES


Cdninperu

Recommended Posts

Just installed a Growatt SPF 5000es into my system I had a Sigineer 5000H and they both have the same problem they won’t charge the batteries. Good voltage coming from the array supplying ac to the house but won’t charge. 48v flooded batteries 

Link to comment
Share on other sites

Thanks for the response. If I run the generator the solar will go to charge the batteries as the gen supplies the ac load. If I don’t run the gen the solar and batteries only supply the ac load. Is there a way to set it so the solar charges the batteries as the first priority? That’s what my old one did. It would always charge the batteries first. 

Link to comment
Share on other sites

Your Solar voltage at 131,5V. Is this in daytime? How many panels have you got and what is their configuration and specs?
This inverter has a MPPT startup voltage of 150V + or - 10V
State all your program settings from 01 through to 23
 

Edited by zsde
Link to comment
Share on other sites

9 hours ago, Cdninperu said:

3 panel strings on this array

Then I am afraid that may be your problem. You did not provide the panel specs. 
If your array was wired as 3S 3P then both your previous and current Inverter will basically not have enough Voltage from the panels to operate consistently.
Lets assume your panels are 40V VOC. That would give you around 120V for a 3 panel string.
This Inverter MPPT operates  between 120-430V DC with a startup of 150V.
Not knowing your panel specs and working an the assumed 40VDC, you should string all 9 panels in series which would then give you ~360V. 

Edited by zsde
Link to comment
Share on other sites

2 minutes ago, Cdninperu said:

changed my array to 3x6

I am glad you got it sorted, but surely that can't be 3 X 6. You have 9 panels you said.
Your best option remains a 9 panel series string.

Link to comment
Share on other sites

Sorry that was a brain malfunction I have two array’s. One is 18x 370 watt panels 48.2voc they were in 3 panel strings now in 6 panel strings. Pointing north at 22degrees I’m in the southern Amazon jungle in peru. I am charging 16 6v 600ah ultracell flooded batteries. I also have an Outback charge control connected to another string of 9x 445w 48.9 voc panels. These I have pointing west to grab the latest sun of the day to top off the batteries. Thanks again for the help! 

Edited by Cdninperu
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...