June 19, 20233 yr Struggling to find a user manual for any of these breakers. Specifically: https://hager.com/intl-en/products/information/mjn725-mcb-1pn-45ka-c-25a-1m I know CBI list their breakers and earth leakages as "Suitable to use for electrical isolation" I assume that means they can be reconnected under load, just not sure if Hager is the same?
June 19, 20233 yr Author @JustinSchoeman thank you. I don't see mention of on load reconnecting though, so presumably an isolator is still required or are there some that can also do reconnects under load? But then the typical domestic person is usually taught to isolate after trips before re-engaging the breaker 🤔
June 19, 20233 yr 5 minutes ago, rinners said: @JustinSchoeman But then the typical domestic person is usually taught to isolate after trips before re-engaging the breaker 🤔 But for isolators it will also be switching under no load. Generally my gut says you can close under load when the MCB can break the load. Perhaps my gut is wrong??? Edited June 19, 20233 yr by Scorp007
June 19, 20233 yr There is no separate rating or requirement for reconnection. (Looking at the IEC definitions, a circuit breaker must be rated for on and off load operation in both senses.)
June 19, 20233 yr Author 21 minutes ago, Scorp007 said: But for isolators it will also be switching under no load. Generally my gut says you can close under load when the MCB can break the load. Perhaps my gut is wrong??? What about in rush current?
June 19, 20233 yr There is a fault current stipulated on each breaker normally in "kA" that is the fault current the breaker could carry before it is destroyed. @rinnersyou Hager breaker has a fault carrying capacity of 4000 amps.
June 19, 20233 yr 5 minutes ago, TaliaB said: There is a fault current stipulated on each breaker normally in "kA" that is the fault current the breaker could carry before it is destroyed. @rinnersyou Hager breaker has a fault carrying capacity of 4000 amps. One of the test you do before signing off the CoC PFC( prospective fault current) test calculates the current that will flow in the event of an earth fault; i.e., Line to Earth. It is important that we conduct the tests to make sure that the protective devices installed within a circuit are rated at the correct breaking capacity. Within a domestic installation, it is common to find 6000A (6kA) rated MCB’s installed within a circuit Edited June 19, 20233 yr by TaliaB
June 19, 20233 yr 1 hour ago, rinners said: What about in rush current? Never will the inrush current exceed the rating of the breaker. Lowest class I think is 2500A. Edited June 19, 20233 yr by Scorp007
July 20, 20233 yr 8 minutes ago, Superfly said: Isolating from the breaker is much better IMHO. You might not find the breaker. People even build DB inside a kitchen cupboard with no notice. Just like people build inverters inside kitchen cupboards. I'm not even talking about the free space around a DB as per regs.
July 20, 20233 yr 59 minutes ago, Superfly said: not sure why the regs specify an isolator within a certain distance for stoves and geysers Both geyser and stove isolators breaking live and neutral(2pole) within 1.5 meters from the appliance. Stove wiring size 4mm² so you need dedicated 32 amp breaker from the db and 40 amp isolator. If it is a standard 4 plate stove with oven then you can not run it off a 16 amp socket outlet.
July 21, 20233 yr 9 hours ago, Superfly said: True, didn't think of that - I suppose it stems from non-socketed connections - both my stove and geyser run off sockets (heatpump) so I did not connect isolators... need to get CoC - will see ... not that's it's a big deal to install the isolator... just saying. Also very practical. A guy needs to work on the heat pump and perhaps switch it on/off a few times. If rainy no muddy boots through your house as he might not even have to enter the house :). Although an added expense I see just good in it.