Can Hager breakers be used as isolators

Featured Replies

  • Author

@JustinSchoeman thank you.

I don't see mention of on load reconnecting though, so presumably an isolator is still required or are there some that can also do reconnects under load?

But then the typical domestic person is usually taught to isolate after trips before re-engaging the breaker 🤔

5 minutes ago, rinners said:

@JustinSchoeman

But then the typical domestic person is usually taught to isolate after trips before re-engaging the breaker 🤔

But for isolators it will also be switching under no load. Generally my gut says you can close under load when the MCB can break the load. Perhaps my gut is wrong??? 

 

Edited by Scorp007

  • Author
21 minutes ago, Scorp007 said:

But for isolators it will also be switching under no load. Generally my gut says you can close under load when the MCB can break the load. Perhaps my gut is wrong??? 

 

What about in rush current?

There is a fault current stipulated on each breaker normally in "kA" that is the fault current the breaker could carry before it is destroyed. @rinnersyou Hager breaker has a fault carrying capacity of 4000 amps. 

5 minutes ago, TaliaB said:

There is a fault current stipulated on each breaker normally in "kA" that is the fault current the breaker could carry before it is destroyed. @rinnersyou Hager breaker has a fault carrying capacity of 4000 amps. 

One of the test you do before signing off the CoC  PFC( prospective fault current) test calculates the current that will flow in the event of an earth fault; i.e., Line to Earth.

It is important that we conduct the tests to make sure that the protective devices installed within a circuit are rated at the correct breaking capacity. Within a domestic installation, it is common to find 6000A (6kA) rated MCB’s installed within a circuit

Edited by TaliaB

  • 1 month later...
8 minutes ago, Superfly said:

Isolating from the breaker is much better IMHO.

You might not find the breaker. People even build DB inside a kitchen cupboard with no notice. Just like people build inverters inside kitchen cupboards. 

I'm not even talking about the free space around a DB as per regs. 

59 minutes ago, Superfly said:

not sure why the regs specify an isolator within a certain distance for stoves and geysers

Both geyser and stove isolators breaking live and neutral(2pole) within 1.5 meters from the appliance. Stove wiring size 4mm² so you need dedicated 32 amp breaker from the db and 40 amp isolator. If it is a standard 4 plate stove with oven then you can not run it off a 16 amp socket outlet.

9 hours ago, Superfly said:

True, didn't think of that - I suppose it stems from non-socketed connections - both my stove and geyser run off sockets (heatpump) so I did not connect isolators... need to get CoC - will see ... not that's it's a big deal to install the isolator... just saying.

Also very practical. A guy needs to work on the heat pump and perhaps switch it on/off a few times. 

If rainy no muddy boots through your house as he might not even have to enter the house :). Although an added expense I see just good in it. 

 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.