July 22, 20233 yr Hi All, I just installed my system: 1 x Deye 5kW Inverter | 1 x 48v 100Ah 5.1kWh Lithium Iron Phosphate LVTopSun Battery | 8 x 550W SunSolar Solar Panels. I am still trying to work it all out, but this is what I currently have setup (images). I am really keen to run as much as possible from the battery.... I see a long delay when it switches back to grid (about 1 minute)? I this normal? I am waiting for my Solar Assistant to arrive... Best Regards Jean
July 22, 20233 yr 20 minutes ago, Jean Vos said: Hi All, I just installed my system: 1 x Deye 5kW Inverter | 1 x 48v 100Ah 5.1kWh Lithium Iron Phosphate LVTopSun Battery | 8 x 550W SunSolar Solar Panels. I am still trying to work it all out, but this is what I currently have setup (images). I am really keen to run as much as possible from the battery.... I see a long delay when it switches back to grid (about 1 minute)? I this normal? I am waiting for my Solar Assistant to arrive... Best Regards Jean From your timer settings to keep the battery at 95% from 16h30 to 21h00 means you will be using grid power. You are only using battery power from 21h00 to 08h00 and this is 55% of battery capacity. Thus less than 3kWh per day. Very little used for self use by keeping the battery at 95% during the day period when there is sun. Normally one would try and use all the sun available as this is where one gets a high saving. To me priority is to use PV 1st and the battery for after sunset and ready for LS. Some members will be in a better position to give you guidelines. Just my 2c based on your settings. Edited July 22, 20233 yr by Scorp007
July 22, 20233 yr Author So I dont think I understand this. If at all possible and you have a moment, please send me the breakdown of all 6 lines of what you would recommend and when the "Grid Charge". must be ticked. I would really appreciate any help I can get... Best Regards Jean
July 22, 20233 yr On the understanding that this is your battery: https://www.lvtopsun.com/lvtopsun-lifepo4-lithium-ion-batteries-48v-100ah-deep-cycle-energy-storage-solar-battery-p3935502.html Try this. Very much open to tweaking. But it has a certain logic behind it. As summer comes you can push the grid-charge slot later in the day. X Time of Use Grid Charge Gen Time Power Batt 00:00 04:00 2400 40% 04:00 08:00 2400 30% 08:00 15:00 2400 100% X 15:00 17:00 2400 70% 17:00 21:00 2400 60% 21:00 00:00 2400 50% Max A Charge: 50A Max A Discharge: 100A Grid charge: 50A Grid Low Voltage: 207V Grid High Voltage: 253V Battery Shutdown: 10% Battery Warning: 15% Battery re-start: 30% Energy Pattern: Load First And together with that, schedule as much as possible of your loads to run during the middle of the day, eg geysers, pool pumps, laundry, dishwasher, anything that happens to have a timer setting on it, sequence them to run one after the other between around 9am-3pm. On the understanding that your heavy consumers like geysers are connected as non-essential loads. Edited July 22, 20233 yr by GreenFields
July 23, 20233 yr Author 19 hours ago, GreenFields said: On the understanding that this is your battery: https://www.lvtopsun.com/lvtopsun-lifepo4-lithium-ion-batteries-48v-100ah-deep-cycle-energy-storage-solar-battery-p3935502.html Try this. Very much open to tweaking. But it has a certain logic behind it. As summer comes you can push the grid-charge slot later in the day. X Time of Use Grid Charge Gen Time Power Batt 00:00 04:00 2400 40% 04:00 08:00 2400 30% 08:00 15:00 2400 100% X 15:00 17:00 2400 70% 17:00 21:00 2400 60% 21:00 00:00 2400 50% Max A Charge: 50A Max A Discharge: 100A Grid charge: 50A Grid Low Voltage: 207V Grid High Voltage: 253V Battery Shutdown: 10% Battery Warning: 15% Battery re-start: 30% Energy Pattern: Load First And together with that, schedule as much as possible of your loads to run during the middle of the day, eg geysers, pool pumps, laundry, dishwasher, anything that happens to have a timer setting on it, sequence them to run one after the other between around 9am-3pm. On the understanding that your heavy consumers like geysers are connected as non-essential loads. ThankYou! Yes it is that battery. A few questions about this if you dont mind: 1. Power column: What does this mean? My inverter is 5kv. Default setting is 5000... 2. Line 5: Does this mean if the battery is not at 100% by 15, charge with the grid to 70%? If so, I have sun until about 17:00. Can I set to charge from 17:00. Can I up the 70% to say 80%? 3. "Energy Pattern: Load First" What if I set it to "Battery First"? Thjaks Again! Regards Jean
July 23, 20233 yr 52 minutes ago, Jean Vos said: ThankYou! Yes it is that battery. A few questions about this if you dont mind: 1. Power column: What does this mean? My inverter is 5kv. Default setting is 5000... 2. Line 5: Does this mean if the battery is not at 100% by 15, charge with the grid to 70%? If so, I have sun until about 17:00. Can I set to charge from 17:00. Can I up the 70% to say 80%? 3. "Energy Pattern: Load First" What if I set it to "Battery First"? Thjaks Again! Regards Jean As said, all debatable, open to tweaking, just my 2c. 1. Power column: Looking at the battery specs. Thinking to "baby" the battery during normal on-grid operation. Standard Charge is 50A, which suggests it's more of a 0.5C battery like the Pylontech. Don't know for sure. I know discharge says up to 100A, but you don't need to push the battery that hard to manage to cycle it once a day. Can do that slower throughout the evening. And once the grid goes down the System Work Mode doesn't matter, it defaults back to the battery settings or BMS limits. 2. Yes, you can up the grid charge level to whatever works for you. On sunny days you have comfortably generation to fill the battery. If really bad weather prevented a full charge by 3pm, it's unlikely the rest of the day will give enough power to charge the battery at that time of day. Any sunlight late in the day will also be used anyway. Chose 70% to try to reduce the amount of cycling of grid power, because that pushes up the cost of the grid power due to inefficiency losses. But charging to some reserve for loadshedding is advised. Whatever balance works for you. 3. "Battery First" will set priority for solar energy to charge battery before supplying house loads. Setting to Load First will divert solar power as first priority to your household loads, and charge later, and basically draw less from grid. You should have enough solar panels anyway to charge the battery in-between other daytime load demands.
July 27, 20232 yr Author Hi All! Thanks for all the help so far! I have added another 48v 100Ah Litium battery. This is where I am at with my settings. Any suggestions will be GREATLY appreciated. I think I can be very close to grid free id if I get the settings right? Best Regards Jean Edited July 27, 20232 yr by Jean Vos
July 27, 20232 yr 1 hour ago, Jean Vos said: Hi All! Thanks for all the help so far! I have added another 48v 100Ah Litium battery. This is where I am at with my settings. Any suggestions will be GREATLY appreciated. I think I can be very close to grid free id if I get the settings right? Best Regards Jean Once 20h to 00h is discharged to 30% the 00h to 04h cannot get to 40% without grid charge. I will swop the 2 around. Then also use 30% for the 04h to 08h. Just my input.