Everything posted by GreenFields
-
Off Grid Reno - 12/16kw Deye or Sunsynk?
@DylanP As above, no need for grid-tied hybrid inverters if staying off-grid, maybe two 6kW Deye off-grid inverters, and put the savings towards batteries.
-
Grid-tied inverter vs not
The question of whether to go with AC-Coupling or DC-Coupling should also consider when you will be needing the power. If you're using the power mostly by day, maybe exporting it, or consuming it instantly as it is generated, then it's probably better to go with a grid-tie inverter on the AC (load) side. If you're going to be storing power in the batteries to use later, then it's probably better to go with an MPPT on the DC (battery) side. The difference is in how many DC-AC and AC-DC conversions you will be doing, ie. efficiency plays a role. But it's also taking into account that the inverter's rated capacity is likely to be the bottleneck in your system.
-
Kwikot Elon Smart - please check my work
Two main concerns. First is is to understand the total energy requirements better regarding generation and storage ie. when does the Kilawatt show your current heating of 11kWh is taking place, day and/or night, and will the system be able to generate and store enough total energy you need, in whatever size geyser size you have on hand, to cover evening and morning hot water needs. Worst case if you've got say a 150l geyser and it gets heated up effectively for 1.5-2 hrs during the day, then emptied in the evening, and re-filled cold, and heated for another 1.5-2 hrs during the evening, you should check whether daytime-only heating is going to produce the real-world savings you're looking for. Second concern, is why you are looking to use an unapproved panel configuration. Just reading through the Elon manual, it's quite extensive in its listing of recommended/prohibited/sub-optimal panel arrangements, and says that any alternative setups should be checked with them. My concern is, even if it works technically, that they may not support warranty claims on panels that they didn't agree to. Also, just looking through the manual regarding energy requirements for various cities, it seems you'd be better off in Durban to go with around 3kW of panels, probably in a parallel configuration as per the manual. Side-comment: Having 3kW of the same panels once-off is also "safer" to upgrade with, ie. to transfer to one MPPT of a 5-6kW inverter later, without having to mix and match panels. I understand that financing is a constraint, and I love the idea of not paying a premium, but I also hate waste and risk.
-
Upgrade Your Old Pylontech Batteries – Exclusive Trade-In Offer with Solar Deity & Powerforum!
I saw that comment, which is fair enough of what's been happening locally in the past. But I'd guess that the new local rep of a battery manufacturer could have access to international recycling facilities, if they can gather up enough of the local stock through a buyback programme to make exporting it worthwhile. Not saying this is what they are doing, but I think the business model could be workable, considering that they are also selling new product in its place.
-
Upgrade Your Old Pylontech Batteries – Exclusive Trade-In Offer with Solar Deity & Powerforum!
Okay, so then the R2K on offer (approx $120 USD) is about middle of the road or average for the reported international scrap value of the battery. Just stating the obvious. I'm sure the newer batteries are better and more desirable, but each one must maar decide for himself how much his old generation battery is still worth to him.
-
Upgrade Your Old Pylontech Batteries – Exclusive Trade-In Offer with Solar Deity & Powerforum!
Out of interest I just did a Google search using the words: "48v 75ah lithium battery raw material value in us$" and got the AI answer: "The raw material value for a 48V 75Ah (approx. 3.6 kWh) lithium iron phosphate (LFP) battery is roughly $220 to $300 USD, based on average cell-level LFP raw material and commodity benchmarks" I make allowance that this may be inaccurate, but for sure I'd want to dig deeper before thinking even for a second of selling some fully functional built up batteries for possibly half the cost of the materials used to make it. Don't care, not leaping before looking.
-
Power4Less Omnivolt G2 Hybrid Inverter (Details and Review)
Some other stats worth noting. Maximum Open Circuit Voltage is 500V - never exceed this value. Other thing is that the battery charge spec is a maximum continuous charge of 100A, but a recommended charge of 40A (0.2C), while the solar charger can handle 200A. The BMS seems to allow 200A surge discharge for 16 seconds if I'm reading right (subject to correction). I suppose it is what it is and it does what it says on the box, but I'd have liked a higher continuous battery charge/discharge rate to support the rated 10kW for longer in the absence of the sun, if this is being sold as an all-in-one 10kW solution. In any case, I think you could re-evaluate if you need the full 10kW of panels with 200A charge capability, if the battery can't handle it. Personally I'd install just 5.5kW at first, say 2.75kW per PV input, or say 5x550W panels per PV input, and then later evaluate if you want more. Depends on the rest of your daytime loads.
-
Winter & heaters running off Solar system
For surviving on minimal power, a 400W wall panel heater per room, then close interleading doors and only heat the rooms you need. Or electric blankets.
-
8kw Deye (2025) + 3 Greenrich WM500 Batteries + 12 620w Canadian Solar BiFacials
The Smart load uses a separate port. Please confirm, or check whether the geyser is connected to the "GEN" port on the underside of the inverter. It might be that it's just connected as a non-essential load, ie. on the Main switch as a household load, but excluded from the backed up home circuits on the LOAD port.
-
sunsynk 8kw 3phase hybrid 2 inverters in parallel 8 x10kwh sunket batteries
Please confirm your inverter model, and the type of grid supply or wiring layout. I can't find any info on an 8kW 3-phase Sunsynk inverter (assuming you meant kW not kWh). Or are you saying that you have 2x single-phase inverters, each connected on one phase within a 3-phase power network? What phase(s) are your loads on, and which are the inverters on?
-
Help with Inverter settings
This issue cannot be resolved with a connection or a setting. It is a characteristic of the panel that is not optimal for the inverter's charger type. Also, considering that the house is already facing around 20 degrees East, those panels are actually facing a bit towards South-East, further reducing the generation capacity. Would there be too many shadows if you fit them to the main roof facing North-East? Unfortunately you've got a complex situation with possibly no easy solutions.
-
Help with Inverter settings
Layman's 2c, use at own risk, or get advice. Some points to consider all the same. You've got an inverter with a 1200W PWM charge controller. In Winter that's just not quite enough to keep the battery charged. On average, touch and go, under the best of conditions in Winter, it's just-just sort of okay, but most of the time not, and if you're intending to run daytime loads from it as well, then you just don't have enough power generation capability. On top of that your setup is likely not optimal to begin with. I'm assuming that your 2 x panels are connected in parallel, or it would have exceeded the inverter's max VOC and caused a failure. If this is not already in parallel, you really should change it over to parallel. But your panel's Vmp isn't ideally matched to the inverter. Better would have been to use a panel like the Canadian Solar HiKU6 CS6W405MS panel (x3), because the Vmp spec is better aligned with the battery charging Voltage. Unfortunately you've got a 25% loss of efficiency with the current panel right out the gate. You could lower the discharge cut-off Voltage to 20V (spec as per the battery), ie. discharge it deeper than the inverter is doing now. And then I think you should change from SBU mode to utility mode, ie. just keep the battery and panels on-hand as a loadshedding solution, without trying to power the whole house from it permanently. You'd have to do a more drastic upgrade, like changing to a 24V MPPT-controlled inverter, and adding maybe another two panels, before you can start thinking of running daytime base load and then still charging the battery by day for draining at night.
-
Adding 2 panels to a 6.6kWp E/W split on a 5kW Sunsynk for winter — safe and worth it?
Given the East/West split, you won't see the full 7.7kWp anyway, the peak should be lowered to around 7kW at mid-day in high summer (you can check it on an online solar calculator). Maybe calculate by another route and compare it to your current mid-day peak in summer, then add another 17% on-top of that. I'm not in a position to give a comment on the safety.
-
EXPECTED PV GENERATION IN WINTER - INSTALLED VS OUTPUT
Winter solstice was just 3 days ago, so ja, poor power generation is still basically the worst right now that it will be all year. But the 1000W on a panel set of 4360W sounds like too little. What's the Voltage and Current on PV2? Around 250V and 4A? Do you generate any more on PV2 if the PV1 string is disconnected? Do you have any problems with shade being cast over that 2nd string?
-
Charge limits
Doesn't sound immediately like an issue, just the info communicated by the batteries (BMS) to the inverter. Sounds like 3x105A discharge rate, ie. 105A discharge spec per battery.And the charge rate may vary depending on how fully charged the batteries are. But in any case if you have just the one inverter you'd have a peak charge rate from grid of around 120A-150A give or take, just guesstimating. And around 110A from panels. So you'll basically never put stress on the batteries. Money wasted unless there is a clear sign of a fault.
-
Solar power calc
You could check whether a 24V Victron Multiplus setup would work for you, but in the long run it's a strong consideration to transition to 48V or even HV batteries, if you want to increase the system power. What exact batteries have you got, and what's the spec for lifespan or number of cycles ? That might also help guide the level of expense to incur now for the 24V path. Maybe you could look at options for the best use-case, if you would dedicate this 24V / 3.5kW / 20kWh system to a feed a specific 15A sub-circuit in the house, and get a different 48V inverter system to feed the main circuit breaker. Similar to how you have an MPPT dedicated to a geyser. Meaning, maybe use this exclusively for running an aircon, or a pool pump, or get an electric vehicle.
-
Deye inverters time of use (power) setting question
Please try that for yourself and let me know. The last time I did that I had a residual usage of around 50-60W from my battery, but I may well have issues with inaccuracies because of my CT-coil cable length. If you set it to zero and really get exactly zero, I'd love to know.
-
Deye inverters time of use (power) setting question
This is unusual. The "Power" column specifically restricts the amount of power supplied from the battery. Try to change the end time for that slot, ie. don't let your time slots all end at 00:00, split it up to end say at 9pm for Time4, then end at 10pm for Time 5. No guarantee that this will resolve the issue, but I've got a similar setup that also limits my power drawn at various times in the evening (eg. when my geyser timer is running), and it works well like that. Maybe double-check that the system time on the inverter is perfectly correct, although looking at your screenshot and posting time, it might not be the real issue either.
-
Honest solar payback calculator.
Generally love it. Point of feedback, maybe a thought to display the SA map of daily peak sun hours, as an indication of how much sun hours one can expect in different parts of the country. And extend the inputs range to around 6.5 hrs to include major towns in the North-West part of the country like Upington.
-
LBSA Low Voltage Batteries - Power That Grows With Your Needs
Batteries look interesting. Installation looks very neat, but does it meet the inverter manufacturer's requirement for ventilation space on all sides of the inverter, if you are covering the bottom up to hide the cabling? Just my first thought, don't know the answer, and I'm too lazy to look it up. I just know I wouldn't want a warranty to be invalidated if it turns out it's not installed according to the manual.
-
What controls your battery charging current?
Yes, the batteries are rated 1C charge according to the spec sheets, to take 105A each, so then if you charge at 100A that the inverter can handle, they will will still be charging at around 50A each, ie. well within in the battery manufacturer's spec. Basically at a 0.5C rate. But I'd set the inverter charge rate to 80A as a balance between going easy on your system (batteries as well as inverter), and extracting useful performance. That's around 0.4C or 4kW charging power, in your setup, on a panel set of just over 5kW. Any less, like if you're using a 50A charge rate on the inverter, then you'd be negating a fair bit of the benefit of having that many panels in the first place.
-
New to Solar - Trying to decide how best to spec a system
This is very close to the type of setup I was referring to in a previous post. Sorry, have to repeat this: it's a great setup for someone who needs more autonomy from the grid. But if you've got low usage of 15-20kWh daily, and typically under 6kW of peak power, then you could cut this system basically in half, I guess for around half the price, and still have a system that will meet your power needs 95% of the time (okay, I'm making that number up, but you get the point), as long as you stay grid-connected. And if you then still want to go more off-grid, then the logical upgrade path will be to buy the other half of the system.
-
Newbie looking at starting with a Deye system
If you are keen on fitting panels to the South-West roof, even if it's sub-optimal, bear in mind that the 12kW inverter has got three MPPT's, which can also take parallel strings. You could therefore combine your orange and red strings onto the first MPPT, two six-strings in parallel, leaving an MPPT free for the South-West side. Maybe you might struggle to fit at least 4 of the 600W panels, but if you could say fit 4, but better 5 of the 450W panels to MPPT3 facing SW, that could plausibly work.
-
New to Solar - Trying to decide how best to spec a system
Or else go with a 6kW Solis hybrid at the start, with just one 15kWh battery and 8x600W panels on just one MPPT, and keep the non-essentials on the grid side but powered from the inverter too. That's for a more cost-effective more grid-tied start-up that you could scale up by doubling everything up. Even if you don't, it should already go a long way towards covering the 15-20kWh daily usage with 6kW peak usage on most days. Your usage is not actually that much that a smaller system couldn't handle most of it even if it's sometimes a squeeze. How often is the grid out in your area, though? I'd be leaning towards the 12kW inverter and doubling from the start if grid-independence is the main immediate concern.
-
Flat Plate Solar Collector on top of roof, geyser inside roof. Is a pump really necessary?
Please don't delete the question, you never know if maybe someone else comes looking for the same answers in the future. I want to say, though, that not everyone necessarily has the same experience. I've had my flat plate split system now for nigh on 10 years, and my pump has never given in. The panel itself has had a 10-year warranty, so maybe I should start expecting hassles soon, but so far it's been plain sailing. The only gripe is that it is not as effective in Winter as in summer, but it still helps by reducing the amount of top-up heating needed.