Buying much more electricity compared to SUNSYNK app

Featured Replies

3 hours ago, Bobster. said:

Also by now it would be known, and there would be shielding in the cables or instructions to run them on separate conduits. 

ISTM The most common problem we find here with Deye/Sunsynk is CT coils the wrong way around. Which I don't think is a Sunsynk thing, it's just because that is such a common inverter here. 

May be it's just me but I find a wrong polarity CT is purely on the shoulder of the installer. The manual is clear on this. The fact that different inverters have the arrow in different directions is not the makers mistake. 

I assisted a forum member when his major installer in a Western Cape large town/city indicated that no inverter can work with PV only and grid and must have a battery just shows the the depth of interest of some installers. 

Edited by Scorp007

2 hours ago, Scorp007 said:

May be it's just me but I find a wrong polarity CT is purely on the shoulder of the installer. The manual is clear on this. The fact that different inverters have the arrow in different directions is not the makers mistake. 

I assisted a forum member when his major installer in a Western Cape large town/city indicated that no inverter can work with PV only and grid and must have a battery just shows the the depth of interest of some installers. 

I think you're right. The CTs don't install themselves.

 

6 minutes ago, Kingsway said:

IMG_3882.jpeg

From this we see a 107W being exported on the C phase. This is not prevented by the CT. So my call remains a CT wrong way connected. This is being charged as power used by the prepaid meter. 

Edited by Scorp007

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.