April 14, 20242 yr I have a 5kw DEYE inverter coupled to 2 stage 1 VOLTA batteries, the system runs everything in the house except gysers and stove. and would like to upgrade. My options are to get another 5KW DEYE or 8Kw Sunsynk inverter. Which is the better option.
April 14, 20242 yr Get another 5kW in parallel. That provides redundancy should one of them be faulty over and above the 10kW load capability
April 15, 20242 yr Author 12 hours ago, zsde said: Get another 5kW in parallel. That provides redundancy should one of them be faulty over and above the 10kW load capability Can I mix brands and get a 5kw sunsynk?
April 15, 20242 yr Normally you can only parallel the exact same model of Inverter, that is, the Inverter has to have the necessary comms and load sharing boards and Firmware that facilitates the paralleling.
April 15, 20242 yr Author 51 minutes ago, zsde said: Normally you can only parallel the exact same model of Inverter, that is, the Inverter has to have the necessary comms and load sharing boards and Firmware that facilitates the paralleling. So when the inverters are in parallel does that mean that they can run loads which are beyond 5KW or do I need to split the loads between the 2 inverters?
April 15, 20242 yr Two 5kW inverters in parallel will give you 10kW. The load is shared between the two.
April 15, 20242 yr Author What will appear on the inverter(s) screen When the combined load goes beyond 5KW?
April 15, 20242 yr Each inverter will still be limited by it's individual power limits Not sure how the DEYE display looks like in parallel mode but all that happens on for example my Growatt is the one displays HST (Host) and the subsequent ones are SL1, SL2 etc, depending how many you parellel. If you have a load of 5kW each inverter will supply around 2,5kW, it shares the load at roughly 50% of the total on each inverter.
April 15, 20242 yr Just now, NINJARO said: So if I have a load of 8KW they wont trip? No. Each one would supply around 4kW. Here is a snapshot of my two Inverters sharing the load. This is from my monitoring software. You will see the total load and then the roughly 50% of that load supplied by each inverter
April 15, 20242 yr 2 hours ago, NINJARO said: Can I mix brands and get a 5kw sunsynk? I wouldn't, getting after sales support from Sunsynk is russian roulette these days. Stick with another Deye