Inverter wiring problem


ShaunKZN

Recommended Posts

Hi all 

My electrician has been trying to hook up my inverter to the DB for 2 days now and no luck. I have a 3 phase system and trying to power up 1 phase(Blue phase).

When I turn my Changeover switch to inverter mode(switch position 2) , the earth leakage on the main DB drops IF eskom power is on, but if Eskom power is OFF then the earth leakage stays on and my batteries power the phase.

When I turn my changeover to Eskom supply (Position 1) , earth leakage stays up and I'm getting supply from eskom.

Problem is , I've got to go manually change the switch during loadshedding.

Can the experts please have a look at the way it is connected and advise.
 
 

Inverter.jpg

1.JPG

2.jpg

3.jpg

Link to comment
Share on other sites

Are you sure Neutral Bar 1 is fed from BEFORE the RCD and not after it? Neutral bars are typically connected after the RCD. If that is the case, your Axpert's live side is possibly fed before RCD and the neutral after it. Easy mistake to make.

Link to comment
Share on other sites

There is more wrong with this. What the heck is going on with Neutral bar 2? That is fed from the grid-side RCD, as well as by the inverter, with the changeover apparently just switching it back on itself (ie doing nothing). Wired like this, the bypass switch in the inverter is also bypassing the neutral on the RCD. No wonder it is tripping.

May I humbly suggest a different electrician? Is that being too forward? 😛

 

Link to comment
Share on other sites

Also,

That yellow wire with the ugly strip-frayed insulation, that is temporary right? Obviously no good in a finished installation 🙂

Red wire from neutral bar to changeover... wutt?

The blue wire going around the red/yellow to get to the earth bar... blue for earth?! And it looks like it is only 1.5mm^2. Earth must be sized for the full fault current.

Edited by plonkster
Link to comment
Share on other sites

Hi guys, I purchased a Mecer kv5 inverter hot wired with stove thickness cable to a plug that is directly connected to the DB board so has no other load(I think its a 10 gauge) I have no battery nor PV as source only Eskom but the unit does not power up. What can it be? Regards Mr A

Link to comment
Share on other sites

1 hour ago, ShaunKZN said:

Lol next time you down for a project swing by 🍺

You are lucky. Wait till his OCD / ADD / ACC / HTTP kicks in ... @plonkster hates things not being neat and tidy. 🙂 

Link to comment
Share on other sites

2 hours ago, The Terrible Triplett said:

hates things not being neat and tidy

That's the weird thing. I am equally good at cutting a corner, sticking on band aids, procrastinating, and so on and so forth. When I was a sysadmin I would leave some "lesser" security updates for later (remote exploits are important... but local exploits aren't anything to lose sleep over... you need access to the machine already to run one of those, so you're already in trouble at that point). In any case, despite all this, I am amazed to find that my attitude to such things still rank just south of OCD compared to some others... 🙂

 

Link to comment
Share on other sites

10 hours ago, Mr.A said:

I have no battery

All models except those from around 2013 need battery power to even light the display. [ Edit: except those very few new models that advertise operation without a battery. ]

Edited by Coulomb
Link to comment
Share on other sites

Got a new electrician to come around today. He spent an hour , and its fixed! 

He says he has to clean the box up a bit but it should be working fine. He says my changeover switch was reading voltage even in the "off" position.

 

Here's what it looks like now.

 

image1.thumb.jpeg.27f88f5ce351ca466a08a2339a4ba1b8.jpeg

Link to comment
Share on other sites

  • 4 years later...

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...