April 27Apr 27 Hello,I have recently acquired two used Luxpower LXP 12K hybrid inverters, mainly because they are capable of operating in closed loop mode, with “older US series” Pylontech battery modules, which was an initial concern.My new concern is the built in MPPT charger. I have always preferred an independent standalone MPPT charger, but since the Luxpower already has 3+1 MPPTs built in (MPPT 1 is capable of running 2 equal strings) independent circuits rated @ 31A/19A/19A IOC which is great, but then I noticed that the ISC rating is 25A/15A/15A. The issue is that I already have 20) 635W bifacial panels that are rated @ 17.4 ISC and 16.6 IMP.As I understand it, Luxpower inverters are considered fairly decent, but I would rather not take an uneducated guess, and assume that 2 additional amps, would not cause any problems and instead possibly overload or worse, damage either or both inverters…There is not a lot of information regarding the LXP-LB series; although I read that if running the latest Firmware, that the PV would be capable of operating at 17A. I am running build version faab-2525 and LCD version 01/23.can anyone possibly confirm this, or wether it is possible to operate at 17A without potential damage? I know that the recommended MCBs are 20A per each individual string if so configuredany information or assistance is greatly appreciated. Thanks_Loch Edited April 27Apr 27 by Loch
April 27Apr 27 41 minutes ago, Loch said:Hello,I have recently acquired two used Luxpower LXP 12K hybrid inverters, mainly because they are capable of operating in closed loop mode, with “older US series” Pylontech battery modules, which was an initial concern.My new concern is the built in MPPT charger. I have always preferred an independent standalone MPPT charger, but since the Luxpower already has 3+1 MPPTs built in (MPPT 1 is capable of running 2 equal strings) independent circuits rated @ 31A/19A/19A IOC which is great, but then I noticed that the ISC rating is 25A/15A/15A. The issue is that I already have 20) 635W bifacial panels that are rated @ 17.4 ISC and 16.6 IMP.As I understand it, Luxpower inverters are considered fairly decent, but I would rather not take an uneducated guess, and assume that 2 additional amps, would not cause any problems and instead possibly overload or worse, damage either or both inverters…There is not a lot of information regarding the LXP-LB series; although I read that if running the latest Firmware, that the PV would be capable of operating at 17A. I am running build version faab-2525 and LCD version 01/23.can anyone possibly confirm this, or wether it is possible to operate at 17A without potential damage? I know that the recommended MCBs are 20A per each individual string if so configuredany information or assistance is greatly appreciated. Thanks_LochGreat inverters these. Just do the upgrade before you start. A few years ago some Luxpowers would just switch off if ever you exceeded the power side with no damage. Just ensure you stick to below the Voc of the strings and downgrade the string voltage to the lowest temp in your area in winter.
April 28Apr 28 10 hours ago, Loch said:Hello,I have recently acquired two used Luxpower LXP 12K hybrid inverters, mainly because they are capable of operating in closed loop mode, with “older US series” Pylontech battery modules, which was an initial concern.My new concern is the built in MPPT charger. I have always preferred an independent standalone MPPT charger, but since the Luxpower already has 3+1 MPPTs built in (MPPT 1 is capable of running 2 equal strings) independent circuits rated @ 31A/19A/19A IOC which is great, but then I noticed that the ISC rating is 25A/15A/15A. The issue is that I already have 20) 635W bifacial panels that are rated @ 17.4 ISC and 16.6 IMP.As I understand it, Luxpower inverters are considered fairly decent, but I would rather not take an uneducated guess, and assume that 2 additional amps, would not cause any problems and instead possibly overload or worse, damage either or both inverters…There is not a lot of information regarding the LXP-LB series; although I read that if running the latest Firmware, that the PV would be capable of operating at 17A. I am running build version faab-2525 and LCD version 01/23.can anyone possibly confirm this, or wether it is possible to operate at 17A without potential damage? I know that the recommended MCBs are 20A per each individual string if so configuredany information or assistance is greatly appreciated. Thanks_LochJust to concur to your information above. These are decent designed inverters and any Mppt worth their salt would protect itself on overcurrent( clipping)The rating on the Lux Mppt's is:Max usable current is 25/15/15 meaning any current above the said spesification will be clipped. The short curcuit current of the Mppt's is 34/17/17 above the nominal working current.... the 17A would not be an issue as the 2A om Mppt 2 and Mppt 3 would be clipped without any damage as @Scorp007 said just keep your Voc below 450v.https://luxpowertek.com/wp-content/uploads/2024/10/LXP-LB-EU-12K-User-Manual-24.10.11.pdf Edited April 28Apr 28 by TaliaB
April 28Apr 28 3 hours ago, TaliaB said:Just to concur to your information above. These are decent designed inverters and any Mppt worth their salt would protect itself on overcurrent( clipping)The rating on the Lux Mppt's is:Max usable current is 25/15/15 meaning any current above the said spesification will be clipped. The short curcuit current of the Mppt's is 34/17/17 above the nominal working current.... the 17A would not be an issue as the 2A om Mppt 2 and Mppt 3 would be clipped without any damage as @Scorp007 said just keep your Voc below 450v.https://luxpowertek.com/wp-content/uploads/2024/10/LXP-LB-EU-12K-User-Manual-24.10.11.pdfIt seems the firmware on the specs provided by @Loch for the older model was ISC for panels were 31/19/19A. If 2strings of ISC of 17A were connected and the inverter fails and a claim was submitted and Luxpower insist on pictures of the panel specs and find it at 34A could they not refuse a claim based on the ISC that was exceeded?@TaliaB
April 28Apr 28 17 hours ago, Loch said:but since the Luxpower already has 3+1 MPPTs built in (MPPT 1 is capable of running 2 equal strings) independent circuits ratedMaybe I misunderstood the highlighted part of @Loch question. My reasoning the inverter with 3 Mppt's are rated for 18kw. 20 x 635w =12.7kw. Spread the strings 8 panels on Mppt1 (8S1P), Mppt 2 6 panels (6S1P) and Mppt 3 (6S1P) then the ISC rating is honoured. Mppt will then theoretical clip 2 amps each(Mppt 2&3) if 17Amps is ever reached.3 hours ago, Scorp007 said:If 2strings of ISC of 17A were connected and the inverter failsYou can not configure 10S2P on Mppt 1 You exceed voltage and current limits.3 hours ago, Scorp007 said:
April 28Apr 28 45 minutes ago, TaliaB said:Maybe I misunderstood the highlighted part of @Loch question. My reasoning the inverter with 3 Mppt's are rated for 18kw. 20 x 635w =12.7kw. Spread the strings 8 panels on Mppt1 (8S1P), Mppt 2 6 panels (6S1P) and Mppt 3 (6S1P) then the ISC rating is honoured. Mppt will then theoretical clip 2 amps each(Mppt 2&3) if 17Amps is ever reached.You can not configure 10S2P on Mppt 1 You exceed voltage and current limits.Thanks for clarifying how to use the 20 panels. My mistake by thinking one can use -?S2P for the MPPT that is good for 31/34A.I only zoomed in that area. So this leaves us that one will not be able to use 2 parallel strings for the indicated panels due to exceeding the 31A if on the old firmware. +1 for information. I sometimes wonder why such a good inverter never caught the attention in SA
April 28Apr 28 Author Hello all,Great information and advisory on a software update(s), prior to placing units into service. I am relieved to know that any additional current would be clipped. While rated at 500v, It doesn’t seem reasonable to operate at a maximum rating, and I am more than affable in operating the PV at 400VDC to 450VDC, as I do not have any specifics, at the moment, on how the bifacial operational characteristics might affect the inverter’s design and operating parameters. This is a bit of uncharted territory, where low voltage high current standalone MPPTs were what I knew to be efficient (or thought I knew). Excellent explanations, questions I too have wondered, spot on reasoning and resourcesThank you @Scorp007 ,and @TaliaB again for the excellent feedback and sound logic and advice The bifacial factor; I am not sure that I fully understand its intended effect, though based on some additional research, if I understood correctly, can yield additional energy under perfect conditions and/or depending on how it is installed. I have also read that it can simplify the manufacturing process but I do not profess to be an expert, as I am fairly new to solar in general. There are some overlapping concepts, that are rooted in science such as ohm’s law and watt’s law that I have a reasonable understanding of. In my test setup, the panels are not exactly roof mounted due to weight, the concept of being situated in the so called historic “red roof district” Kings Qtr. and the prospect of geographically residing within a trajectory along the Atlantic Ocean, where hurricanes can be quite devastating (i.e., Irma and Maria; August of 2017). Hurricane season begins on the 1st of July to the end of November. Being on the opposite hemisphere, North is the only coordinal direction generally avoided.Attached are the exact panel ratings Thank you kindly,_Loch
April 28Apr 28 Author 2 hours ago, TaliaB said:Maybe I misunderstood the highlighted part of @Loch question. My reasoning the inverter with 3 Mppt's are rated for 18kw. 20 x 635w =12.7kw. This. I did not quite understand why the current rating was lower than say a solark inverter, where the PV current is rated at 26/26/26 @ 500VDC and yet the MPPTs are limited to 19k, but at the same time, the Luxpower MPPTs are rated to 18k at 31/15/15.There seems to be a discrepancy with some maths somewhere… or maybe not 🤔 I remember when solark was initially introduced; it started out as a 12K unit but later became a 15k unit. The reasoning was somewhere along the lines of intentionally de-rating the unit, I think largely due to possible liability? After sufficient testing, the 12k became the 15k with a software update. Of course with that said, 12k x 2 is more power than I would ever use as one individual; I don’t think that I even consume 5k at a given time, washer/dryer aside. Gas stove are the basic standard, locally, but if not, still my preference, the original wood burning brick oven is still in tact but I do not intend to fire it up, lest to cook on a auto ignition gas stove period. Aircon is something that I have been debating; though with very high ceilings and very large windows; It seems a bit much. The ceiling fans works well with the pass though to the outer courtyard. Those older Danish Sommerhus were built purely out of practicality; even if a bit of an overkill in some respects.
April 28Apr 28 7 minutes ago, Loch said:This. I did not quite understand why the current rating was lower than say a solark inverter, where the PV current is rated at 26/26/26 @ 500VDC and yet the MPPTs are limited to 19k, but at the same time, the Luxpower MPPTs are rated to 18k at 31/15/15.There seems to be a discrepancy with some maths somewhere… or maybe not 🤔 I remember when solark was initially introduced; it started out as a 12K unit but later became a 15k unit. The reasoning was somewhere along the lines of intentionally de-rating the unit, I think largely due to possible liability? After sufficient testing, the 12k became the 15k with a software update.Of course with that said, 12k x 2 is more power than I would ever use as one individual; I don’t think that I even consume 5k at a given time, washer/dryer aside. Gas stove are the basic standard, locally, but if not, still my preference, the original wood burning brick oven is still in tact but I do not intend to fire it up, lest to cook on a auto ignition gas stove period. Aircon is something that I have been debating; though with very high ceilings and very large windows; It seems a bit much. The ceiling fans works well with the pass though to the outer courtyard. Those older Danish Sommerhus were built purely out of practicality; even if a bit of an overkill in some respects.Thanks for providing the panel specs. From that we can calculate that allowing a 8% rise from the Voc that even 10 panels in series only brings the string Voc to 491V. For my safety margin I would not use more than 9 in a series string. Not at all an input as to how you use your 20 panels but more around the discussion @TaliaB and I had earlier when talking about 2 strings in parallel for MPPT1 when I had a blond moment. His way of connecting the 20 panels still holds as a good way of using them.
April 28Apr 28 2 hours ago, Loch said:geographically residing within a trajectory along the Atlantic Ocean, where hurricanes can be quite devastating (i.e., Irma and Maria; August of 2017). Hurricane season begins on the 1st of July to the end of NovemberCould you please confirm your geographical location? That’s important when advising on solar design and selecting the most appropriate setup.From your description, it sounds like you may be in the Caribbean region (e.g. Bahamas or nearby islands). If that’s the case, ambient temperatures remain relatively high year-round, so cold-temperature Voc increases are minimal and generally not a limiting factor in array design.
April 30Apr 30 Author Hi,@TaliaB I am primarily located in the U.S. Virgin Islands; formerly known as the Danish West Indies (as of 1917). Yes you are correct; a part of the Caribbean; Lesser Antilles. Thank you for that bit of information. So if I understood correctly, the bifacial component has no significance in overall design; at least not in this region?_Loch
April 30Apr 30 Author On 2026/04/28 at 1:52 PM, Scorp007 said:Thanks for providing the panel specs. From that we can calculate that allowing a 8% rise from the Voc that even 10 panels in series only brings the string Voc to 491V. For my safety margin I would not use more than 9 in a series string.Not at all an input as to how you use your 20 panels but more around the discussion @TaliaB and I had earlier when talking about 2 strings in parallel for MPPT1 when I had a blond moment. His way of connecting the 20 panels still holds as a good way of using them.Copy that 👍
May 3May 3 Author Hello It appears that there is so much information regarding PV that I truly had little to no understanding of. Of course this is still a bit of a steep learning curve, but I think that the basler principles and functions are better understood. I was always of the opinion that the higher the current output DC the better; contrary to, it seems that higher current output, can lead to a shorter system lifespan, as opposed to a higher voltage system which is more predictable and constant, as opposed to a higher current, which may be more prone to fluctuations throughout the day. At the end of the day, power is power (total watts) no matter the configuration. After a bit more research, (x) S1P, (x) S2P, or even expressed as: (x) P2S; although the prior is a cleaner expression. I am of the opinion that higher wattage panels are a bit more difficult to configure and where shading can be a bit more problematic opposed to a comparable array, utilizing lower wattage panels. Besides the advantages in a more flexible configuration; subtracting the bifacial component, which two panes of glass have a tremendous effect on weight, with little to no additional gains, at least in my region. I now know why they have been in stock for such a long time, with the remaining panels being still available. Originally I bought 8) 440w panels;and by the end of the week, when I was “satisfied” with the initial layout, factored weight, cable routing and “power calculations” all 440w panels were already completely out of stock; ALL 12 PALLETS!!! I could not believe this; it seemed too incredulous at the time. What I needed and wanted was one panel style; having read a vast number of posts regarding mixing panels. sure, more 440s would eventually return to stock, but in a different format or form factor.I was then told about this 1 pallet of 635w panels that were in stock; just 1. My question was how long would they remain; but assured that all 31 panels would be available for sale. It sounded perfect, but naturally being a bit wary, the decision to purchase the 20 at once, really more than intended, seemed like the safe and sensible thing to do. In a way it was, because the remainder 635s are all still available for purchase. But I now know why: no sensible individual would ever put 20 to 30 panels 1400 LBS plus 700LBS (over 1 ton) or ironically 635kg plus 317.5kg, NOT including racking, on their existing roof, unless it was priorly reinforced or constructed to handle that much additional weight. Having once lived in a place where it snowed heavily to the point that the front door would be frozen shut at times; where the water pipes occasionally froze shut even when insulated and wrapped with pipe heaters; when the smart thing to do was simply leave the faucets open just enough to discourage blockage or potential damage from expansion, and presumably where roofs are built to intentionally withstand that extra weight, without caving in; assuming that you would clear it off after a snowstorm; both ends of the spectrum still would not favor that added weight on any roof unless in a commercial application, but preferably a low mounted installation, or a carefully designated “roof”. Balconies, galleries or porches are intentionally designed, “engineered” and constructed “to separate” from the main structure, without significantly damaging the main structure in the event of a serious hurricane: the above listed “appendages” while unified in appearance, are completely separate roofs in a heavy, pegged post and beam type, arrangement. The independent ring beam is attached a beam that is attached to the main structure with square cut nails; now with a few reproduction nails and are meant to break under extreme conditions… the existing was in need of some repairs and additional reinforcement. To my relief it has weathered the tests of time quite well; being that the square cut nails were hand wrought and intact and the planking, and the the rafters were still “heartwood” pine; the proposed repairs were sympathetic; to graft and splice only the minor section of rot with green treated lumber but it was stressed over and over again by the contractor that it must give unless I want the easterly “wing” to be damaged or worse in a likely scenario. With shallow pockets, we scrapped the idea of The “glass ceiling effect” that the solar panels would impart mostly because of the already unforeseen exorbitant costs, often associated with DIY projects, I am very appreciative of his lengthy explanation, as well as his expertise and knowledge in construction, as well as his bright enthusiasm, where he showed me some roman numerals carved into the rafters where short sections of planking were sectioned from “a single piece of wood of that length ””indicating non dimensional lumber and confirmation of age based upon the cross-hatched saw marks and forged nails” I should have taken some photographs, but I am sure that he did. I know that this is a power forum, not exactly a construction forum.If anything that I have learned during this process is: the cheap becomes extremely expensive very quickly, especially during these times. _Loch
May 3May 3 Author …It was my sole intentions to say (or rather demonstrate to a few associates of mine) that solar energy can be affordably had; even at a sight budget. Not all equipment has to be brand new, and that a system can be designed to be expanded upon. I know that it is possible, but I chose the wrong methodology to convey this 😑plus this does not help the cause. Yes, this it is very repairable but I can’t say that, en masse; electronics repair is just a former hobby at this point; where in the past, most consumer electronics were repaired NOT replaced as in the present. There are no repair shops locally, and shipping it off to the manufacturer is not an option. Warranties on these units are seldom honoured. If so, the local retailer on island would have already had them repaired or replaced under warranty, presumably, and not sell both units for next to nothing. The other unit had a problem; it did not appear so except the RSD alarm would not go away. I would not consider that a problem, as it powered up without any trace of the magic smoke. The solution: its safety jumper was in the terminal block of the dry contacts in the wrong place; a short piece of red wire with a tag that reads: “Remove it in installation”. Source of repair: The installation manual which states to put it back after installation. Time spent troubleshooting: about an hour. I grew up learning not to be wasteful regardless, and if something is broken; fix it rather than discarding it. For a small oversight, that Luxpower unit is fully functional. The other unit… that one was a bit of a surprise, I do not even see any tool marks on the hex allen head lugs. After removing the breaker/relay board and the battery breaker, did I catch a whiff of the magic smoke 😑 then the upper circuit board, and there it was 🤬 Until I remove both transformers; the top to source a suitable replacement, the bottom which visibly is done or rather “well done” bad pun I know; test the diodes, resistor network (not likely but relative to potential above ground ) and presumably IGBTS or MOSFETS below, as well as the rest of the relevant circuitry, I can not say with certainty what caused this: something as simple as reverse polarity improper input or, a software based feature that I am not particularly fond of, regarding toggling the GEN input to a smart output or a point of AC coupling PV... Because this is the immediate DC board to the batteries, all AC sources are called in to question. In general, most if not all control circuits in this unit are DC. Looking at the relay board and breaker for LOAD , I know that the primary control voltage is 12VDC since those relays are activated by 12VDC, which controls the GRID and PASSTHROUGH: 12VDC coil and 200A @ 830VAC. (The GRID input can be toggled to a GENERATOR input). The FPGA control board, touchscreen comm board and control circuits are DC. I am fairly certain that there are also a 3.3?, 5, 24 VDC rails. Note: I am pleasantly surprised to see a number of high quality components in this unit: rubycon capacitors, Texas Instruments FPGA; airpax style breakers, big solid lugs and “ground planes”, heavy high current busses, an abnormally large amount of filtering /smoothing capacitors, lots of opt coupling and isolation, which really begs the question? WTH happened? How was this accomplished?The diodes appear to be rectifying some AC source via a small step down transformer to DC, which is likely coupled to smothing capacitors to power up the control circuits; these hybrid units do not like to be operated without the batteries connected; it is not impossible but the manuals for most inverters have a startup sequence, and a shutdown sequence. Not that I am stating something that everyone is likely more familiar with than I am.What I am not fond of is that the software does not forcibly disable toggles that would otherwise conflict and cause damage, which is clearly stated when selecting the smart output option; rather than simply disabling or deselecting the conflicting commands. But then again, the input/output values can be zeroed out for the most part but it can be too easy to make a mistake even after reading the manual in detail. I am not impervious to mistakes; I knocked out my MPPT charge controller with reverse polarity, even though it has reverse polarity protection: just not while it is loaded with PV energy; but fortunate to have a backup while I repaired it; it blew a MOV but not quick enough before it blew an IGBT. The shorted IGBT caused the charge controller to keep rebooting in a circular. It functioned fine after removing the failed IGBT (there are 6 of them in parallel) so in effect, it only temporarily reduced it’s capacity, until all 6 were replaced for uniformity and good measure.Anyhow, I do not believe in waste; it is not trash or a spare parts unit (unless proven otherwise in the unlikely probability). With that said. There is a power supply much like this on each board: the inverter board, the MPPT board, this main DC board and so forth. To be continued…
May 3May 3 Author This is the working unit; after figuring out how to make the older pylontech batteries communicate with it; I did not want to cut my Victron cable and opted to temporarily used a coupler and a small patch cable to figure out which one is (can h) and (can l); on this inverter, there is no (can gnd). Turns out that it is a straight through connection ONLY with pins 4 (can h) and pins 5 (can l). ***Correction*** Dip switch position on the Pylontech batteries does NOT appear to matter when using the CANbus port! Note: The initial sequence of operation may, at least to make it recognizable, but also, a few incongruities or glitches have been noted with the Luxpower unit; but appeared to correct itself after removing the CMOS battery for about 10 minutes or until completely discharged. The DIP SWs does not appear to have any effect whatsoever on “recognition” or any thing to do with the Canbus in general. My apologies; the very last thing that I want, is to perpetuate false information; but rather reciprocate the appropriate information.This thread might serve better in the |new to solar| section…The start up sequence of operation did appear to have a positive effect on what was intended: to make the older US series Pylontech batteries connect to the Luxpower inverter. I can only offer suggestion on what worked for me; nothing more. Being exhausted and dozing off in between, and a tangent later, is not proper for lucid conveyance of information. For this, you have my apologies.The sequence of events that appeared to establish CANbus communication was:1) fabricate or acquire an appropriate communications cable. In this case, the Luxpower LXP series inverter, and the pylontech US series CANbus utilize the same twisted pair; pin nr. 4 is CAN H and is the striped-blue wire. Pin nr. 5 is CAN L and is the solid blue wire. Both ends are configured exactly like this. Note: My initial problem was defining pin nr. 1 as a reference. The manual(s) are a bit ambiguous, or perhaps it was just my misunderstanding. This is determined from the contact side and NOT from the keyway side as recently learned. Not so interesting, the very opposite was the method and way I was priorly taught. The problem with this method is that the terminated pins in this instance, are in the reverse order; which presumably may cause damage in some instances where power is also transmitted. Networking 101, I presume…2) Where DIP SW position is irrelevant, to the best of my revised understanding; all DIP switches on all Pylontech modules are now in the off position, by personal preference. It is recommended to power off all batteries before making these changes. Connect only the battery side of the communications cable and restart all batteries.3) Set the inverter to lithium, and the following drop down menu to: nr. 2 lithium (Pylontech).4) Restart or power on the inverter; it is recommended to leave the load and PV switch off, for the time being. After the inverter has fully booted and the main screen is displayed then plug in the other end of the communications cable. Recognition took about a minute or so. Note: this method worked for me, where I could not establish communication any other way. Mileage may vary, and perhaps there is another way to achieve successful communication between inverter and battery BMS via CANbus.5) If successful, the inverter will not throw a comm error alarm. This can be ascertained within 2 minutes. To confirm, under stats and then battery, It will show the correct SOC/SOH, BATT CAPACITY, VCELLMAX/VCELLMIN as well as a VCHARGE/VCUT OF 53.2VDC/40.0VDC. These are set to 52.5VDC and 44.0VDC respectively, for my specific application, but also per the manufacturer’s recommended operating range.6) Older Luxpower inverters are pins 3 and 4; this was a bit confusing because there are a t least one factory datasheet in circulation that appears to be misleading. The colour of the dip switches changed 3 times: “V1 is red, V2 is blue and V3 is red”. V2 and V3 utilize pins 4 and 5, but V1 utilize pins 3 and 4. <sighs> when in doubt, the manual specific to the unit is almost always correct… 95% of the time, unless a new revision, or software update states otherwise. _Loch Edited May 5May 5 by Loch Further corrected for the conveyance of accurate information.
May 4May 4 Author Ok. so this is not at all what it initially appeared to be: the first thing that came to mind after complete removal was that it sort of had an uncanny appearance to the main board of a VFD. This is most likely a 3 level NPC board of sorts. 12 MOSFETS total; 6 drivers, which controls two MOSFETS in a pair. One high, one low. Both high frequency ferrite gate drive switching transformers share the same power source from the modulated driver output to common nodes (2), one node branches to both GDTs; the other node also branches to both GDTs but with two anti feedback diodes, to protect the GDT modulated driver from inductive backfeed to the driver, where the cathode is facing each transformer, presumably. Both GDT transformer outputs are common to all 3 levels: TXA, TXB and TXC and their respective FET Drivers. Bat + and - have been traced directly to the 26pin ribbon connector header, as well as a presumed feedback circuit from each level. Apologies for the poor explanation; not exactly my strong point. I Imagine that the unit would have most likely power up, but with a critical failure. It is generally good practice not to energize any device or circuit without basic verification, as this can lead to further damage and/or injury to self and others…Simply put, this is a deceptively simple circuit for my current repair knowledge library; or maybe not. Certain concepts and principles are slowly coming back to me (it’s complicated). However, being that only one GDT clearly failed; the truth is, that even without a schematic, which I am not certain is essential at this point, for this particular instance; where the sequential process of elimination, to repair are fairly straightforward. Next step is to check the diodes for a short circuit, where one seems likely. At least it is not a multi layer board ***correction*** this is indeed a multilayer board; the section in question is not affected by that fact. The relevant traces can be clearly identified with a backlight. After parts have been tested and removed, will then remove the “silicone” smeared over this area, scrub the board with isopropyl alcohol and a toothbrush, and repair the questionable traces as needed. At this point, there is really nothing to lose; I am certain that Luxpower would have this replacement board on hand, in the event that my repair attempt fails. But I am reasonably confident that this is an isolated incident; I have also noticed some other problem areas; which are more of a manufacturing issue than any thing else. Lead free solder can be problematic at times; A few cold joints, some solder balls and little stray bits of solder have been noted; perfect recipe for a short. On the reverse side, one leg of the transformer looks a bit overheated; which could suggest a cold solder joint, which ultimately failed due to excessive current draw and byproduct of heat. We shall see…It really does look worse than it actually is: after a little cleanup and some board re-work; she’ll be as good as new 😎_Loch Edited May 5May 5 by Loch Corrected for clarity and inaccurate statements
May 5May 5 Author Good morning,After sufficient testing and optical inspection, I am sufficiently satisfied with my findings: 1) All FETS are equal in value and there are no shorted gates. In circuit testing can be challenging when other components have an impact on them. Most tests were performed with an older 8846A, 6.5 digit bench meter. The diode function is especially useful ONLY because it can either check for leakage or other unusual conditions with insertion of 5V or 10v. A microwave diode, for example cannot be tested in this manner, not even at 5v; but it can be tested at 10v. Anyhow, resistance, capacitance and continuity were all valid. The objective is to verify uniformly across all 12 FETs in a number of distinct ways. Yes, connecting the curve tracer would have been much more precise but, not required at this point. I did not suspect a failed FET, but examined none the less for posterity sake.2) All diodes around the GDTs tested ok, then tested again and again with fine tip leeds. No shorts, no open circuits; while mildly surprised; it is reassuring, where the mode of failure is quite consistent with the findings of the optical inspection, via an old M5 stereo microscope. I really REALLY love that scope, it was definitely built with purpose, down to every little detail; all precision machined. I do not mind the turret, eye pieces or objective lens attachments. It is so much nicer, in my personal opinion and experience of course, in contrast to the progressive magnification of the Greenough scope; while convenient, it is harder on the eye, with a quicker onset of fatigue. An absolute dream; those older CMO scopes. Albeit highly underrated... Rarely might I be so enthusiastic, but there is something about yesteryear, worth being passionate about; worth the added effort and dedicated enthusiasm. Moving forward, the smd resistor network, capacitors et al, tested good. Even GDT Transformer (TX2) is still functional. Preliminary Failure mode: a cold solder joint or joints connecting the failed GDT transformer (TX5). Narrative: over the course of non stop operation, that poor connection point(s) builds up resistance until ultimately it simply breaks down from excessive heat and inability to keep up with current draw and supply as pictured. I seriously doubt, but for posterity, I will verify the GDT driver, although if it did fail, by all logic, so should have the other GDT transformer; which tested ok. I cannot find my rework supplies; the burnt trace is detached from the PCB and has been temporarily tacked in place. Nothing major. The pad is still intact but the barrel/sleeve will be replaced and swaged over the reattached pad, for a nice solid connection. The burnt spot will be retouched in PCB green and sealed, as will the exposed traces. Now the literal problem: to source and equivalent set of GDTs. This is the most problematic; sourcing parts without actual or cross referenceable part numbers. As pictured, are some which are identical in package. Even the secondary is identical; unfortunately the primary is not. A difference of 1 ohn might not seem very significant; however the salvaged GDT is approximately 2.5 ohms on the primary. This means that the input voltage would be proportional to the output voltage based on the turns ratio. While the considered replacements secondary is identical, the primary @ less than half of the original, could potentially or rather likely be driven at a higher secondary, and this would most likely cause significant damage to the FET drivers. It would essentially operate at more than twice the expected rating. While there is a small possibility that it might function within range; it does not seem likely and I am not very willing to take that chance, unless tested independently with favourable results. But I Doubt it. Another possibility is: add a 1~1.5 ohm resistor of sufficient wattage to reduce the input voltage to a suitable output level, but a number of variables comes to mind… TBDIdeally I would love to find exact matches for purchase, but without any actual specifics, it is a difficult proposition at the moment, without any further research. If it were a steady state transformer it would not be an issue; I will have to pull out the function generator, assuming it will reach its operating voltage and given frequency; or operate it in reverse; 3.3~5 vin switched to extrapolate these required values, if the GDT driver is too ambiguous, but without researching the driver and its capabilities first, I am merely taking a pss in the dark. I am 100% certain that this board would have failed IPC-610 standards; I did quality control and rework a lifetime ago. Very very nice layout, but the through hole components; the cold solder joints, the foreign and stray residue? The residual flux?The outfit that did PCB manufacturing locally, was sold to Ametek and relocated its manufacturing facility elsewhere. It was the first time that I learned that circuit boards could be submerged in water, or ultrasonically cleaned. They were always scrubbed with a toothbrush after rework that is literally how it is done. There are no special tools for cleaning PCBs. The problem with kester flux or any other flux, especially concerning high speed circuits is that during the test/debug phase, if any residual is present, certain boards would fail under testing: the solution? Back to the wash station; which is similar to a dishwasher, but a very big one. The water was de ionized and heated, which de solved this water based flux, specifically for lead free solder. No tangent… just an observation……still looks worse than it actually is; it is actually so much better than initially imagined. To think that this is the easiest part, if I can remember where I placed my kit. I am sure that most if not all of it is still good; the adhesives and the PCB green polyurethane…_Loch
May 5May 5 Author A bit unrelated: The red arrows indicate a problem, while the yellow are potential defects. A multi-positional ultra high resolution camera could capture the things that are not visible to the naked eye. For each production run, it would be programmed with gerber/BOM data/g-code, but the most m important aspect: defining the fiducials accurately as well as specifics such as rotational defects, polarity defects, component defects and so forth. The bga that was flagged in red is a significant defect, where the bga is incorrectly oriented. I wont elaborate on why, but they were removed and reoriented correctly. A miserable time consuming process. One, no problem, but 4 per panel times 20~30 panels is a disaster. What amounted to a change in procedure. 1 panel is inspected first before a complete production run. Even still…Each and every time. This was by far a tedium; probably the most boring aspect of this relatively small facility, yet one of the most crucial I grew to dislike it, but aside for a deadline, could move to another station; a floater. Eventually was taught how to operate any other station… a simpler time… Thinking about this, It made me wonder: when an inverter fails, what generally happens to it if out of warranty? I know that this definitely varies from region to region; though enquiring minds may find it a curiosity...I can only say that in general that here, a territory of the US, they are wastefully discarded and replaced with a brand new unit; I would say the waste is far greater on the mainland than here, locally. As far as the British side; repair is moreso the preferred route. Yes, I can speak for both, as a multi national. But for curiosity sake? Across the globe?