Breaking +&- from PV, what to use?
Hi there.
I just want to know what the correct way is to isolate your PV strings from the inverter.
Do I break both + and - ?
What should be used to isolate the PV strings? Rotary switch, DC circuit breaker, DC fuse holder or a combination??
At this stage I have used rotary switch and fused on both + and - as well as DC circuit breaker om + only with fuse on both + and - again.
Any help is welcome.
Thanks.
In a DC system, it's perfectly fine to "break" just one input. + is normally broken, though - can be broken as well.
Solar regulations require that we "break" both though. You need to put fuses in for protection, and then an isolator to safely switch disconnect the PV array from the MPPT in case of emergency.
Some MPPT’s like Microcare have built in breakers. Is this acceptable with only fuses, or do they require a separate breaker besides the one in the MPPT?
1 hour ago, DeepBass9 said:
Good question. I have fuses and use the mppt breakers. Interested in the experts opinion!
I recently learnt that I don't need fuses, can just use the NoArk breakers, right sized off course.
The Microcare MPPT I have don't have DC-rated breakers in it. Whether the breakers actually have a DC-rating, that I do not know. Also don't know if newer MPPTs rectified this little oversight (mine is from 2013). I rather doubt that the breakers are sufficient. I can't find any info on it, they are "Crabtree SB2" units with a 230VAC rating indicated.
I see the newer ones have Chint breakers. I know some of them (Chint ones) have DC ratings.