Axpert inverter low battery warning even though pylontech batteries are fully charged.

Featured Replies

Hi, 

our system is as follows. 
10 x 330w panels leading into an Axpert 5kva inverter powered by 2 x 2.4kw pylontech batteries. 
 

I have used the settings recommended in this forum for the pylontech batteries but my problem is this. 
 

the pylontech batteries show fully charged or almost fully charged yet the Axpert inverter is issuing a code 4 warning saying the batteries are low. 
not sure how to make sure the inverter and the batteries register the same charge? 

  • Author

29 is at 47.5v

Inverter is a year old.Axpert 5kva 4kw model. 
 

inverter linked to batteries by 2 power cables and the communication cable going into the CAN port on the master battery. 
 

no monitoring as no idea how to do that :( 

If you can change setting 5 to PYL with that black cable (have other settings actually), black cable might not work. Try to change setting 05 to PYL, need to see if your inverter have that setting.

otherwise to get rid of error 04, set 29 to 45.5, the alarm actually buzz at setting 29+ 2v, which is too high IMO. I run mine at 45.5v and have 0 issues, battery never go lower than 30% before PV starts charging it in the morning.

Edited by Wilfred

https://powerforum.co.za/topic/2519-mpp-solar-inverters-support-pylontech-some-models/?do=findComment&comment=64538

I know they say everywhere 48v or 47.5v, problem is, your batteries will most likely run at 49v 99% of the time, the BMS will shut it down at around 10% SOC and should actually go back to grid at around 22% SOC, without any monitoring software or anything. 
setting 27 should also be same as setting 26. The Axperts use voltage to determine SOC and it is actually way off measuring it that way.

setting 29 at 45.5v will be fine as you have 12 at 48. The battery should be at 48v for a while before it will go to grid.

  • Author

Thanks for your help everyone. 
seems to have worked with lowering setting 29 down to 45.5. 

Thanks centurion solar - very insightful and will be in touch. 
 

thanks again 
 

 

Edited by Phillip1

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.