Posted February 27, 20205 yr Hie I have 5 phocos 5KVA inverters connected in parallel in a 3 phase system where by I have two inverters per phase and the remaining phase one inverter. the inverters are charging fine with solar panels but how ever they are rejecting the ac input even though it is in range (230V). Batteries are pylontech and 10 of them connected to a common bus bar what could be the possible cause?
February 28, 20205 yr Could it be a phase rotation issue? The inverters will be looking for a particular phase sequence. Try changing setting 28, swap any pair e.g. P2 and P3. This setting uniquely requires the power switch to be off. I'd isolate the outputs, and check for low voltage across the output isolater before switching back on. With three phases, there is so much more opportunity for splat followed by oops 😮
February 28, 20205 yr 9 minutes ago, Coulomb said: there is so much more opportunity for splat followed by oops 😮 I have a new favourite quote, thanks! 😂