Axpert_MKSII-5KVA error 57


Moallam
 Share

Question

Hi

I installed an inverter Axpert_MKSII-5KVA, and after two days of operation the inverter stopped working and error 57 was displayed. Which means in the User Guide (current Sensor failed).

What causes this error? How can it be fixed?

Link to comment
Share on other sites

5 answers to this question

Recommended Posts

  • 0
5 hours ago, Moallam said:

What causes this error?

It could be excessive bias (measured current at start-up when the current should be zero) from one or more of four current sensors:

  • output (load) current (there is a current transformer, it looks a bit like an audio transformer)
  • inverter current (an LEM hall effect sensor I believe)
  • output current sharing sensor (might be on the paralleling board? You could try removing that temporarily if you have one)
  • the DC2DC current sensor. I believe that this is something unique to models with the 450 V max MPPTs, so I don't know anything about them.

Unless you have an unusual load which has asymmetrical current (hair dryer on half power?), it doesn't look like something you can repair yourself. Perhaps attempt to demagnetise the CT or LEM, but that's about it.

Failing any of the above, it looks like you'll have to get it repaired or replaced under warranty, and I'd say it would be a main-board replacement. This is the most expensive part of the inverter-charger. It sounds like it's brand new (two days of service?), so unless you have any nasty loads, it looks like you should be able to get a warranty replacement. Unfortunately, with high demand and the COVID-19 situation, it may take some time to get resolved.

Link to comment
Share on other sites

  • 0

Hie. Having the same error. Two transistors were blown around SG3525, a MOSFET(smd) and a bipolar driver. Changed 2 reservoir caps 470uF/450v. One of them was swollen. Also removed the communication board that was water damaged. Still the error persists. Also changed SG3525 but no change. What could I be missing?

Link to comment
Share on other sites

  • 0
On 2020/05/01 at 12:21 AM, Mazwi said:

What could I be missing?

It could be the sensors themselves. But more likely, check the burden resistor for the current transformer. This post mentions a successful repair, though the symptom was error 07 (fault code 07): overload timeout. Also the op-amps (or possibly comparators) and associated components on the control board (perhaps pins 3 and 4 for output current).

Link to comment
Share on other sites

  • 0

I recently repaired a board that had this same error . The board was damaged by a leaking pipe that dripped water onto the inverter through the ceiling which then shorted out the DC bus. AC IGBTs, DC MOSFETs were blown and replaced. Error 57 continued and the problem turned out to be one of the transistors that drive the DC  MOSFETs. It had short circuited and was pulling up the -12V power rail that the HTC sensor needs. So your problem might not be this exact transistor but check the power supply to the sensor.

DSC_2376.jpg

DSC_2375.jpg

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Answer this question...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...