Please HElp with settings

Featured Replies

Good day all.

Hope you can help me.

We recently decided to bite the bullet and do solar.I was wondering if anyone could assist me with getting the settings right on my system.

We have the following:

4 x Pylontech US3000 3.5KW Batteries

12 x JA Solar 300W Mono Panels

1 x Axpert HYbrid 5000W Inverter

1 x Rasperry Pi

We have changed all lights to LED. Have Solar geyser and have left the oven on Eskom Grid.Some days early morning system switches off completely.Does not revert to Grid to get power.

 

Please help.

 

Regards

 

Piet van der Westhuizen

 

 

Hi Piet

it sounds like your Pylons are getting drained to the point where they shut down - which means that the setpoint for the Axpert to switch back to Utility is set too low.

When you say that you have a Pi, does that also mean that you are running ICC? And do you also have the cable to connect the Pylons to the Pi?

If you are running ICC, then we can set everything through there. If not, we will need to go through the individual settings on your Axpert.

Please post answers to my questions above - and then we will take it from there

 

12 hours ago, Piet van der Westhuizen said:

We recently decided to bite the bullet and do solar.

Welcome to the "solar club" and the forum.

12 hours ago, Piet van der Westhuizen said:

1 x Axpert HYbrid 5000W Inverter

The Axperts aren't actually hybrids, at least per most people's definitions.

Is it a King or VM III like model? If so, you can use a special cable to the battery to get better control.

12 hours ago, Piet van der Westhuizen said:

1 x Rasperry Pi

Does it have monitoring firmware like ICC yet?

Here is my latest, ever changing pylontech settings cheat sheet, assuming you don't or can't use the special cable. For you, setting 02 will come to 140 A.

 

 

PylonTech settings.png

  • Author
22 hours ago, wolfandy said:

Hi Piet

it sounds like your Pylons are getting drained to the point where they shut down - which means that the setpoint for the Axpert to switch back to Utility is set too low.

When you say that you have a Pi, does that also mean that you are running ICC? And do you also have the cable to connect the Pylons to the Pi?

If you are running ICC, then we can set everything through there. If not, we will need to go through the individual settings on your Axpert.

Please post answers to my questions above - and then we will take it from there

 

HI Andy

 

I do have a cable connected to pylons yes. We have the centurion Solar icc on the pi.

 

Current settings on the Axpert as follows

 

1)

  • Author
Just now, Piet van der Westhuizen said:

HI Andy

 

I do have a cable connected to pylons yes. We have the centurion Solar icc on the pi.

Model name on side of unit:SOL-1-AX-5P

Current settings on the Axpert as follows

 

1)SBU

2) 30 AMP

3)APL

4)SDS

5)USE

6)LTD

7)TRD

9)50HZ

11)10AMP

12)46 VOLT

13)50VOLT

16)CSO

18BON

19)ESP

20)LON

22)AON

23)BYE

25)FEN

26)53.2

27)53.2

28)PAL

29)42 VOLT

30)ONE

31)SBE

32)AUT

33)EDS

34)58.4VOLT

35)60

36)120

37)30D

38)D15

39)ADS

1)

Thanks Piet

Your Back to Grid setting (#12) is too low at 46V. Thereabouts is where the Pylon BMS shuts down to protect itself - which is why your system then completely shut down.

As per @Coulomb recommendation above, you should set this to 48V. But instead of having to do this on the Axpert itself, you can more conveniently do it through ICC. Here are my ICC settings:

ICC-Settings.jpg

As you have 4x Pylons, you can set both Max PV and AC Charging Current to whatever the highest value that it will allow (as long as less than 140A)

You can also increase the Bulk Voltage to 52.5V instead of my 52.5V (I have also done that since this screenshot was taken)

My Back to Discharge value is significantly higher than Coulomb's value as I want ICC to control the switching between battery and utility instead of the Axpert itself

I've found that my SOC-based switching back to utility (see below) typically happens at voltages above 48V, so I leave the Back to Grid Voltage setting at 48V as a safety net

The other very important setting is under the Battery tab:

Battery.jpg

Here you define at which SOC (from Pylon BMS) you want ICC to switch the Axpert. Here you need to experiment a bit. For the To Grid value you need to keep in mind that the Axpert will still draw its self-consumption from the battery even when running on utility. So you need to keep a few % as reserves to make sure that the Axpert's self-consumption does not bring you to below 20% SOC until there sufficient PV to balance the self-consumption. For the To Solar SBU value you need to see at about what time you PV production exceeds your load and what the SOC is at that point (to avoid multiple switching back and forth in the morning)

The other setting that I noticed is #28. If I am not mistaken, you inverter is set to parallel mode. If you are only running a single inverter, I believe you should rather that set to single. If I am not mistaken, you can only change that setting when AC, PV, and loads are disconnected and the inverter is switched off (but batteries still connected). At least that is how it works on my old Axperts

For the rest of the settings I will leave it to our experts ( @Coulomb) to comment if anything else should be changed

Quote

 

Current settings on the Axpert as follows

2) 30 AMP

 

30 amps is very low; that's appropriate for just one Pylontech US3000. Set it to 140 A, even though your present panels will rarely allow more than 70 A of charging.

Quote

12)46 VOLT

13)50VOLT

@wolfandy has already explained these two; thanks, Wolfandy. Fixing these will solve most of your problems.

Quote

 

26)53.2

27)53.2

 

These are the manufacturer's numbers. They're quite high, and have been shown to cause the batteries to switch off at times. Use something like 52.5 V for 26; you can use 52.5 V also for 27 so you don't have to worry about the premature float bug, or use my suggested 51.8 V for slightly longer battery life.

Quote

28)PAL

You only mentioned one inverter; leaving this on PAL (paralleled) can cause weird problems. Change it to SnG (single inverter), but note that you have to have the inverter switched off for this to work. If you have the power on, it will silently fail to change the setting. Have a charging source connected (AC-in and/or solar), so the inverter doesn't completely switch off when you turn off the switch.

Quote

29)42 VOLT

You should change this to 46 V, or 2 V lower than whatever you decide for setting 12.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation

Search

Search

Configure browser push notifications

Chrome (Android)
  1. Tap the lock icon next to the address bar.
  2. Tap Permissions → Notifications.
  3. Adjust your preference.
Chrome (Desktop)
  1. Click the padlock icon in the address bar.
  2. Select Site settings.
  3. Find Notifications and adjust your preference.