Peet Welthagen Posted February 15, 2021 Posted February 15, 2021 Good day, what will be the ideal charging settings for 12 x 200ah lead acid batteries. Connected 4x in series and 3 banks in parallel. I have got 2x Axpert 5000 kva inverters in parallel. Regards Quote
WJP Posted April 24, 2021 Posted April 24, 2021 Can't comment on the voltages but 20 amps per bank, 60amp charge rate in total. Quote
Coulomb Posted April 25, 2021 Posted April 25, 2021 17 hours ago, WJP said: 20 amps per bank, 60amp charge rate in total. That's for a charge rate of 0.1C, which I think is very cautious. Most lead acid batteries can take 0.15C, which would mean 200 x 0.15 = 30 A per paralleled string of battery modules, or 90 A total. The settings of each inverter-charger add, so you could achieve this by setting one to 50 A maximum total charge current, and the other 40 A. Obviously, if one has more or better solar panels connected, make that the one with the 50 A limit. The recommended charge current and voltage should be available in a specification sheet available from the manufacturer (on paper, or more commonly these days on a web page). You didn't say whether the battery modules are sealed, flooded, or AGM. If you leave the battery type setting at AGM, this will charge each 12 V module to 14.1 V, and float at 13.5 V. Those settings are pretty safe for most sealed battery modules. Ironically, actual AGM battery modules usually require higher voltages than that. Quote