November 19, 20214 yr Author 15 hours ago, YellowTapemeasure said: Using the "Select Parameter" button, select (tick) the following boxes: DC Power PV1 DC Power PV2 (if you are using the second MPPT) AC Power R/U/A Grid Frequency Total Grid Power Total Consumption power Battery Power SoC Then post your graph. OK, so I was on a different SolarMan site ?? https://home.solarman.cn/main.html So this is the best I can do (no SoC)
November 19, 20214 yr 14 minutes ago, bobmabena said: OK, so I was on a different SolarMan site ?? https://home.solarman.cn/main.html So this is the best I can do (no SoC) Swop AC Current RUA with AC Power RUA?
November 19, 20214 yr 22 minutes ago, bobmabena said: OK, so I was on a different SolarMan site ?? https://home.solarman.cn/main.html So this is the best I can do (no SoC) Can you also post pics of your setup screens? Was this a cloudy day, or are your panels shaded in any way? Please also post the same graph timeline with (V) DC Voltage PV1, (V) DC Voltage PV2, (A)DC Current 1, (A)DC Current 2, AC Power Total Power (Active) and (W)Battery Power. Edited November 19, 20214 yr by YellowTapemeasure
November 19, 20214 yr Author https://drive.google.com/file/d/1LdCbIfQlESzFJzeXhZkxRiqMb02APYTO/view?usp=sharing all the setting screens are there.
November 19, 20214 yr 5 minutes ago, bobmabena said: https://drive.google.com/file/d/1LdCbIfQlESzFJzeXhZkxRiqMb02APYTO/view?usp=sharing all the setting screens are there. PV voltages look very healthy. and PV was able to supply the spike of 5K at around 13H00 The only time I see it pulling from grid is a tiny blip at 11H00, and then just before and after 15H00. Were there clouds at those times?
November 19, 20214 yr Author 1 minute ago, YellowTapemeasure said: PV voltages look very healthy. and PV was able to supply the spike of 5K at around 13H00 The only time I see it pulling from grid is a tiny blip at 11H00, and then just before and after 15H00. Were there clouds at those times? Nothing... perfectly clear day... I'm just worried that, because this happens almost daily, that it's a sign of a "bigger" issue
November 19, 20214 yr Author Found the SoC selector... as you can see... the battery is fully charged... so I need to know why it's pulling from the grid, and not the battery!
November 19, 20214 yr 8 minutes ago, bobmabena said: Found the SoC selector... as you can see... the battery is fully charged... so I need to know why it's pulling from the grid, and not the battery! Please add (W) AC Output Total Power (Active) to the graph above?
November 19, 20214 yr Interesting that you are limiting battery charge to 40A in the inverter's battery setuo , yet the battery is happy to accept 200A charge (from the LiBMS screen). Also from the LiBMS screen, the batteries are happy to accept a 300A discharge, yet you have them setup as 200Ah? What batteries do you have?
November 19, 20214 yr Author 3 minutes ago, YellowTapemeasure said: Interesting that you are limiting battery charge to 40A in the inverter's battery setuo , yet the battery is happy to accept 200A charge (from the LiBMS screen). Also from the LiBMS screen, the batteries are happy to accept a 300A discharge, yet you have them setup as 200Ah? What batteries do you have? I've got the FreedomWon Lite 10/8, but yes, I see they can charge and discharge at 200A...
November 19, 20214 yr 10 minutes ago, bobmabena said: I've got the FreedomWon Lite 10/8, but yes, I see they can charge and discharge at 200A... Bumping it up to 100A should not hurt it, that's 0.5C I see that max continuous discharge is 240A, 300A is max every 5m per 30m cycle.
November 19, 20214 yr Need the system flow chart and the info screen. Seems that you are exporting to grid a bit. Edited November 19, 20214 yr by YellowTapemeasure
November 19, 20214 yr Did your installer update it to the latest firmware? What is the current version that you are on (hit the gear icon from main screen, then check bottom RH corner).
November 19, 20214 yr 9 minutes ago, YellowTapemeasure said: Need the system flow chart and the info screen. Seems that you are exporting to grid a bit. Need the info screen that looks like this Need to check if the CT value is negative, then it's installed incorrectly. Edited November 19, 20214 yr by YellowTapemeasure
November 19, 20214 yr 24 minutes ago, bobmabena said: Was a semi self install... So no... Versions are e418 and MCU:3878 Latest version is 6006 E41C
November 19, 20214 yr I dont think this would be a firmware issue . Do you have the CT coil installed correctly and on the correct place?